The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 109 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 4 1 2 3 4 >
Topic Options
Rate This Topic
#4461 - 09/28/01 12:42 PM #12 wire Minimum?
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Would you like to see #12 as a minimum wire size for Residential Branch Circuits? Why or Why Not?

Bill

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#4462 - 09/28/01 02:52 PM Re: #12 wire Minimum?
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
Nope.

#1. Waste of resources.

#2. Box fill can become a problem. Hard enough to get compliance in this area as it is.

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#4463 - 09/28/01 03:08 PM Re: #12 wire Minimum?
Fred Offline
Member

Registered: 04/30/01
Posts: 461
Loc: Straughn, IN 47387
In the town I mostly work in, they passed an ordinance in 1996 prohibiting conductors smaller than #12cu in residential buildings for new construction. This became a problem when an addition of manufactured homes was started. They had #14 but had the HUD label.

Top
#4464 - 09/28/01 03:13 PM Re: #12 wire Minimum?
Fred Offline
Member

Registered: 04/30/01
Posts: 461
Loc: Straughn, IN 47387
To answer Bill's question; I rarely used #14 when I was doing residential. Most of my jobs were large custom homes with long home runs. I stuck to 12-2 for voltage drop as much as the convenience of only dealing with one wire size. Box fill wasn't a problem, I never used 1G boxes smaller than 20 cuin. One contractor insisted on 4x4x2-1/8 boxes w/mudrings! I'll play if they pay!

Top
#4465 - 09/28/01 04:37 PM Re: #12 wire Minimum?
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
Fred,

I am sometimes asked to use metal boxes on a Romex job, until they find out how much more it will cost.

I have yet to find a 1 gang plastic box that can handle the following scenario- three wire w/ground home run, 2 two wire cables & a receptacle. If there is a box big enough for this, my suppliers don't carry it.

Box fill is also a problem with multi-gang boxes since there isn't, in my experiance, 20 cubic inches per gang. Of course, maybe I've led a sheltered life.

Naturally, careful wiring layout can overcome the fill problems in some cases, but the multi-gang box is a problem for me since I do not run switch legs down from a light. Tack in a 3 way or two & the multi-gang boxes fill up fast.

Like you, I only buy one size single gang box, the biggest I can get. Cost difference is minimal & the work goes a lot faster.

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#4466 - 09/28/01 05:13 PM Re: #12 wire Minimum?
bordew Offline
Member

Registered: 08/27/01
Posts: 155
Loc: Vienna,Ohio, USA
 Quote:
Originally posted by Fred:
To answer Bill's question; I rarely used #14 when I was doing residential. Most of my jobs were large custom homes with long home runs. I stuck to 12-2 for voltage drop as much as the convenience of only dealing with one wire size. Box fill wasn't a problem, I never used 1G boxes smaller than 20 cuin. One contractor insisted on 4x4x2-1/8 boxes w/mudrings! I'll play if they pay!


Your right, when you start getting into homes with 2500 sq.ft., or more the runs start to become very long and voltage drop can really be a problem. I use the big 4-S too, but if there is a fil problem I will gang 2 x 3 x 3 1/2 together and never have had a problem with it. But as far as limiting the use to just no.12 for residential, I could put up with it, but i'd prefer not to. I do know in the Ccleveland area they can use no wire smaller than No.12, But even with No.12 at about 85 feet and your at the required 5 % voltage drop at 15 amps.

Top
#4467 - 09/28/01 06:08 PM Re: #12 wire Minimum?
sparky66wv Offline
Member

Registered: 11/17/00
Posts: 2339
Loc: West Virginia
I've wired many a home with #12 minimum.

Used CXW 2-1/8" Deep gangable boxes.

Now, I still only use #14 for lighting circuits, all recepts are on #12 with 20A CB's, all pigtailed. Definitely got to put switched recepts on the end of the line, if one wants to go the top-switched bottom-hot split-recept thingee.

I like to put junction boxes to feed hots to switch boxes so that only one hot and no jumpers are taking up space, cramming dimmers into filled-to-the-limit boxes is just too much...

I'll occasionally drop a switch loop if it is convenient, usually it is if the J-box is in an attic.

The house I'm currently wiring has a shop that got EMT and 1-1/2 deep 4x4's (furred with 2" nominal) and plaster rings at 1/2"... Didn't want the DIY homeowner to drive a nail in the Romex when hanging his tools... Had to be real careful with wire count there too...
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

Top
#4468 - 09/28/01 06:21 PM Re: #12 wire Minimum?
Anonymous
Unregistered


I will allow an exception for dedicated alarm circuits to be #14. Circuits that are meant to have receptacles or run lighting should be minimum #12.

1. Inherently more resistant to overloading.
2. Conserves resources.

Here's a killer reason for you:
3. No more backstabbed receptacles!



[This message has been edited by Dspark (edited 09-28-2001).]

Top
#4469 - 09/28/01 08:31 PM Re: #12 wire Minimum?
Jim M Offline
Member

Registered: 08/10/01
Posts: 453
Loc: Chestertown, MD, USA
I have used #12 for most of my work along with 20 cu. in. boxes. With the new vacuums rated at 12 amps it doesn't make sense not to have any reserve in the circuit.

As for box fill try to find the new Carlon Super Blue boxes. They advertise the largest rated capacity and extra rigidity.

Top
#4470 - 09/28/01 09:54 PM Re: #12 wire Minimum?
Dallas Offline
Member

Registered: 08/07/01
Posts: 159
Loc: North Salem, IN 46165
[QUOTE]Originally posted by Tom:
[B]Fred,
I have yet to find a 1 gang plastic box that can handle the following scenario- three wire w/ground home run, 2 two wire cables & a receptacle. If there is a box big enough for this, my suppliers don't carry it.<<

Tom,
The box for what you described is a Carlon (or equiv) 32 cu. in. nail on 4S box, with a 1/2" mud ring. Works out to about 37 or 38 cu. in. total, I think.

In resi, we use #12 minimum for everything. Even lighting circuits, since the few homes we do a year are large customs with a lot of lighting. We try to get around voltage drop by using subpanels where we can.

Top