The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 284 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#44380 - 11/02/04 06:59 PM Living with NFPA 70E
hypress Offline
Member

Registered: 07/20/04
Posts: 132
Loc: Charleston WV
Has anyone had any experience with NFPA70E the electrical safe work procedures and arc blast protection requirements.From what I have heard some of it is OK but some of it is way out in left field. Our plant has been useing flash suits for switching for years now 70E says you have to use flash suits any time you work on anything 100 volts or more.What is your alls take on 70E. THANKS.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#44381 - 11/03/04 04:22 AM Re: Living with NFPA 70E
Big Ed Offline
Member

Registered: 04/07/04
Posts: 56
Loc: Roxboro, NC, USA
Hypress,
It is not as restrictive as that. It stipulates several levels of protection based on the work being done and the voltages present. Basically they have assumed the arc potential for many common jobs and setup the proper protection for each.

I would reccommend that you invest in some arc hazard analysis if you plan on fully implementing 70E, it will significantly lower most of the requirements.

The protection levels can be as low as all-natural fiber clothes up to the full arc suit with ballistic protection.

Good luck,
Ed

Top
#44382 - 11/03/04 07:03 AM Re: Living with NFPA 70E
Ron Offline
Member

Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
In order to use the standardized table in NFPA 70E, you must know the calculated fault current at the equipment you will be working on, then calculate the arc flash fault current, then you can match that to the characteristic of the upstream protective deices (breakers and fuses), to see how long it will take to clear the fault. Then and only then can you attempt to use the table in NFPA 70E, if you fall within the parameters of the notes in the table.
I have found many incident energies higher than 40 or even 100 cal/cm^2, thus making any arc suit useless.
Don't forget the energized work permits required by 70E too
Good luck.