The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 275 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#40218 - 07/14/04 08:56 AM Is this ok?
Lostazhell Offline

Registered: 02/21/04
Posts: 1248
Loc: Bakersfield, CA (Originally Or...
I come across ground wires put together like this constantly.. I always at minimum use a crimp (I also placed a crimp here after the pic)


Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#40219 - 07/14/04 09:17 AM Re: Is this ok?
electricman2 Offline

Registered: 11/09/03
Posts: 234
Loc: Thomasville, NC USA
It doesn't look the wires in the pic were twisted too tightly. I can see between them. 110.14(B) says splices are to be made with devices identified for the use

#40220 - 07/14/04 10:22 AM Re: Is this ok?
ElectricAL Offline

Registered: 10/10/01
Posts: 615
Loc: Minneapolis, MN USA
I'd add a reference to:
250.8 Connection of Grounding and Bonding Equipment.
Grounding conductors and bonding jumpers shall be connected by exothermic welding, listed pressure connectors, listed clamps, or other listed means.
Al Hildenbrand

#40221 - 07/14/04 01:11 PM Re: Is this ok?
CTwireman Offline

Registered: 02/07/02
Posts: 839
Loc: Connecticut, USA
I think a lot of amateurs and professionals alike think "The ground wire doesn't ever do anything, so there is no need for a connector."

Around here, the crimp barrels are pretty popular, but they are often "crimped" incorrectly, that is, just flattened onto the twisted conductors with pliers making for a less than ideal connection.


#40222 - 07/16/04 04:13 AM Re: Is this ok?
velect Offline

Registered: 05/01/04
Posts: 79
Loc: st joseph mi usa
Not enough sheath in the box?

Where the ground is crimped must extend 6 inches out of the box

#40223 - 07/16/04 05:12 AM Re: Is this ok?
earlydean Offline

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
That is: 6 inches of free conductor in the box, 3 inches outside the box. (300.14)