#40218 07/14/04 11:56 AM
Joined: Feb 2004
Posts: 1,438
Member
I come across ground wires put together like this constantly.. I always at minimum use a crimp (I also placed a crimp here after the pic)

[Linked Image from pstr-g02.ygpweb.aol.com]

-Randy

#40219 07/14/04 12:17 PM
Joined: Nov 2003
Posts: 269
E
Member
It doesn't look the wires in the pic were twisted too tightly. I can see between them. 110.14(B) says splices are to be made with devices identified for the use


John
#40220 07/14/04 01:22 PM
Joined: Oct 2001
Posts: 597
E
Member
I'd add a reference to:
Quote
250.8 Connection of Grounding and Bonding Equipment.
Grounding conductors and bonding jumpers shall be connected by exothermic welding, listed pressure connectors, listed clamps, or other listed means.


Al Hildenbrand
#40221 07/14/04 04:11 PM
Joined: Feb 2002
Posts: 840
C
Member
I think a lot of amateurs and professionals alike think "The ground wire doesn't ever do anything, so there is no need for a connector."

Around here, the crimp barrels are pretty popular, but they are often "crimped" incorrectly, that is, just flattened onto the twisted conductors with pliers making for a less than ideal connection.

Peter


Peter
#40222 07/16/04 07:13 AM
Joined: May 2004
Posts: 81
V
Member
Not enough sheath in the box?

Where the ground is crimped must extend 6 inches out of the box

#40223 07/16/04 08:12 AM
Joined: Dec 2003
Posts: 751
E
Member
That is: 6 inches of free conductor in the box, 3 inches outside the box. (300.14)


Earl