The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Yesterday at 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
ghost307 7
HotLine1 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 265 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#3796 - 08/29/01 05:33 AM Grounding
WARREN1 Offline

Registered: 05/09/01
Posts: 184
Loc: Greenville, SC, USA
We are having this discussion on our intranet forum. What do you guys think of this?
In a case where a paralleled feeder using multi-conductor cables and where the standard ground conductor size is not adequate for the OCPD per NEC 250-122. A new properly sized equipment grounding conductor must be installed. Should there be a note to the installer that he/she cut the original (now undersized) equipment grounding conductor back to the jacket and only connect the new adequately sized equipment grounding conductor? Or what would be a better method of installation?

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#3797 - 08/29/01 05:55 AM Re: Grounding
resqcapt19 Offline

Registered: 11/10/00
Posts: 2209
Loc: IL
In my opinion the only options that you have are 1)get a custom cable with the correct size EGC or 2) provide GFP per 250-122(f)(2). If you install an external EGC you would be in violation of 300-3(b).