#3796 - 08/29/01 05:33 AM Grounding
WARREN1 Offline
Member
Registered: 05/09/01
Posts: 176
Loc: Greenville, SC, USA
We are having this discussion on our intranet forum. What do you guys think of this?
In a case where a paralleled feeder using multi-conductor cables and where the standard ground conductor size is not adequate for the OCPD per NEC 250-122. A new properly sized equipment grounding conductor must be installed. Should there be a note to the installer that he/she cut the original (now undersized) equipment grounding conductor back to the jacket and only connect the new adequately sized equipment grounding conductor? Or what would be a better method of installation?
Top
Work Gear for Electricians and the Trades
#3797 - 08/29/01 05:55 AM Re: Grounding
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Warren,
In my opinion the only options that you have are 1)get a custom cable with the correct size EGC or 2) provide GFP per 250-122(f)(2). If you install an external EGC you would be in violation of 300-3(b).
Don(resqcapt19)
_________________________
Don(resqcapt19)
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 61 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals