ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 235 guests, and 27 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#3796 08/29/01 08:33 AM
Joined: May 2001
Posts: 176
W
WARREN1 Offline OP
Member
We are having this discussion on our intranet forum. What do you guys think of this?
In a case where a paralleled feeder using multi-conductor cables and where the standard ground conductor size is not adequate for the OCPD per NEC 250-122. A new properly sized equipment grounding conductor must be installed. Should there be a note to the installer that he/she cut the original (now undersized) equipment grounding conductor back to the jacket and only connect the new adequately sized equipment grounding conductor? Or what would be a better method of installation?

#3797 08/29/01 08:55 AM
Joined: Nov 2000
Posts: 2,148
R
Member
Warren,
In my opinion the only options that you have are 1)get a custom cable with the correct size EGC or 2) provide GFP per 250-122(f)(2). If you install an external EGC you would be in violation of 300-3(b).
Don(resqcapt19)