ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

Topic Options
Rate This Topic
#30717 - 10/26/03 09:14 AM sizing nuetral for M.C.C.
Tim Peters Offline
Member
Registered: 03/08/03
Posts: 10
I have a MCC feeding a 600 amp 277/480 4 wire MCC. I'm using parallel 500mcm for the phases but there is no actuall load on the neutral so can I get away with no neutral? My concern is that the blue prints list it as 4 wire so do you think they want a neutral pulled for future use maybee?

Any info appreciated.
Top
Work Gear for Electricians and the Trades
#30718 - 10/26/03 08:39 PM Re: sizing nuetral for M.C.C.
nesparky Offline
Member
Registered: 06/21/01
Posts: 642
Loc: omaha,ne
Tim
Where is this MCC getting it's control power from?
If the plans and specs call out 4 wire, I would install a full size neutral. You cannot know what is planned for the future unless all the MCC buckets are used now.
_________________________
ed
Top
#30719 - 10/27/03 02:32 AM Re: sizing nuetral for M.C.C.
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
If the plans called for a four wire feeder to this MCC and you bid it and won it with that requirement you should install it.

Putting aside that it is the right thing to do, if after you leave the job they need that neutral who do you think will pay for it to be installed?
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#30720 - 10/27/03 06:13 PM Re: sizing nuetral for M.C.C.
Tim Peters Offline
Member
Registered: 03/08/03
Posts: 10
One bucket of the mcc is feeding a transformer which in turn id feeding a 120/208 panel. This panel is feeding two controll panels for all my controll wiring.
Each bucket of the mcc has a TRF for the coils within it.

I did not bid the job but the nuetral was included in the bid so IMO it should be included but my superiors think different.

This post is mostly meant to justify my thinking, I wanted to make sure I wasnt missing something.
Top
#30721 - 10/27/03 06:19 PM Re: sizing nuetral for M.C.C.
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
I would send an RFI to the engineer and get a CCD on paper to cover your back.
_________________________
Ryan Jackson,
Salt Lake City
Top
#30722 - 10/28/03 03:05 AM Re: sizing nuetral for M.C.C.
zapped208 Offline
Member
Registered: 02/18/03
Posts: 196
Loc: Somewhere in USA
Tim,- Was an equip. gnd. pulled in?, since someone is trying to cut corners on your job?
_________________________
Shoot first, apologize later.....maybe
Top
#30723 - 10/28/03 01:36 PM Re: sizing nuetral for M.C.C.
Tim Peters Offline
Member
Registered: 03/08/03
Posts: 10
Yes a equipment ground will be pulled in
Top
#30724 - 10/28/03 06:40 PM Re: sizing nuetral for M.C.C.
Pinemarten Offline
Member
Registered: 08/23/03
Posts: 123
Loc: Edmonton, AB, Canada
I feel it is up to the owner.
Now cost vs. later. Explain the cost at a later date.
If he wants to save money at this point, he may want to.
I also agree with paper from the engineer, CYA.
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 46 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals