The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by Webmaster
01/17/17 09:41 PM
Re: Fabricating Guards out of Lexan?
by frank
01/17/17 04:11 PM
Would ELV branch circuits be a good idea?
by gfretwell
01/17/17 01:26 PM
Why cables look like they do
by Texas_Ranger
01/17/17 12:33 PM
100% breakers?
by Texas_Ranger
01/16/17 06:13 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 20
Webmaster 19
gfretwell 13
Trumpy 12
ghost307 12
Who's Online
1 registered (Webmaster), 0 Guests and 62 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#27757 - 07/31/03 06:00 PM A/C circuit sizing
CTwireman Offline
Member

Registered: 02/07/02
Posts: 839
Loc: Connecticut, USA
I know this is a "dead horse" topic, but I'm still confused about it. This subject seems to be a source of mass confusion in the electrical trade.

So, as an example, here is an a/c unit nameplate (from an 2 ton Trane unit):

Min circuit ampacity: 15 amps

Min fuse/breaker size: 20 amps

Max fuse/breaker size: 25 amps

Line running amps: 11 amps


Does this mean that the unit can be fed by #14 protected by a 20 amp breaker?

Or #12 on a 20 amp breaker?


Do you size the conductors by the "minimum ampacity," and size the breaker by "minimum fuse/breaker"?

One thing I do understand is that in this situation, the breaker only provides short-circuit protection, as the motor is protected by a thermal overload device.
-Peter
_________________________
Peter

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#27758 - 07/31/03 07:37 PM Re: A/C circuit sizing
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
In this case the code would permit #14 on a 25 amp breaker.
Don
_________________________
Don(resqcapt19)

Top
#27759 - 07/31/03 09:53 PM Re: A/C circuit sizing
elecbob Offline
Member

Registered: 08/23/02
Posts: 142
Loc: WA
A/C unit: 120/208 V 3 phase
Nameplate reads:
18.2 amps FLA.
Min. circuit: 31.5 amps
I had to replace the 30 amp disconnect and #10 wire with a 50 amp disconnect (40 amp disconnect not available) and run #8 wire.

Top
#27760 - 08/01/03 03:52 AM Re: A/C circuit sizing
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Bob,
Were you using NM Cable?
If not, it seems you were in compliance with 310.16, which lists #10 as rated for 35 amps.
As far as having to upsize the disconnect, I think you need to know the Locked Rotor Current so you can back-calculate using Table 430.151(B).

Top
#27761 - 08/01/03 07:25 AM Re: A/C circuit sizing
elecbob Offline
Member

Registered: 08/23/02
Posts: 142
Loc: WA
Thanks Redsy. I was going to pull 4#10's but the inspector said I needed #8 for the 31.5 amps. I was a little suprised to say the least. He is coming out for an inspection on some other gear next week. I will ask him again before I do the pull.

Top
#27762 - 08/01/03 02:01 PM Re: A/C circuit sizing
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Bob,
He may be thinking about the asterisk at the bottom of Table 310.16, which refers to 240.4(D).
However, 240.4(D) refers to 240.4(G), which permits particular Articles to specify conductor ampacity selections.

Top