#27757 07/31/03 09:00 PM
I know this is a "dead horse" topic, but I'm still confused about it. This subject seems to be a source of mass confusion in the electrical trade.
So, as an example, here is an a/c unit nameplate (from an 2 ton Trane unit):
Min circuit ampacity: 15 amps
Min fuse/breaker size: 20 amps
Max fuse/breaker size: 25 amps
Line running amps: 11 amps
Does this mean that the unit can be fed by #14 protected by a 20 amp breaker?
Or #12 on a 20 amp breaker?
Do you size the conductors by the "minimum ampacity," and size the breaker by "minimum fuse/breaker"? [Linked Image]
One thing I do understand is that in this situation, the breaker only provides short-circuit protection, as the motor is protected by a thermal overload device.
-Peter
Peter
#27758 07/31/03 10:37 PM
In this case the code would permit #14 on a 25 amp breaker.
Don
#27759 08/01/03 12:53 AM
A/C unit: 120/208 V 3 phase
Nameplate reads:
18.2 amps FLA.
Min. circuit: 31.5 amps
I had to replace the 30 amp disconnect and #10 wire with a 50 amp disconnect (40 amp disconnect not available) and run #8 wire.
#27760 08/01/03 06:52 AM
Bob,
Were you using NM Cable?
If not, it seems you were in compliance with 310.16, which lists #10 as rated for 35 amps.
As far as having to upsize the disconnect, I think you need to know the Locked Rotor Current so you can back-calculate using Table 430.151(B).
#27761 08/01/03 10:25 AM
Thanks Redsy. I was going to pull 4#10's but the inspector said I needed #8 for the 31.5 amps. I was a little suprised to say the least. He is coming out for an inspection on some other gear next week. I will ask him again before I do the pull.
#27762 08/01/03 05:01 PM
Bob,
He may be thinking about the asterisk at the bottom of Table 310.16, which refers to 240.4(D).
However, 240.4(D) refers to 240.4(G), which permits particular Articles to specify conductor ampacity selections.