#261 - 01/05/01 05:11 AM SQ. D GFI Circuit Breaker
Bob Hinshaw Offline
Junior Member
Registered: 01/05/01
Posts: 5
Loc: Tipp City, Ohio, USA
I have a 15 amp GFI circuit breaker that trips everytime the microwave oven is started. The microwave is not on the same circuit as the cb, and no matter what circuit in the house or garage I plug the microwave in, when it is turned on it trips the cb. If the microwave is off, everything works fine. I have changed out the GFI cb with a new one and it still does it. The only way it will work, is with a standard cb. Also, with the microwave plugged in a GFI receptacle, it does not trip it, but will still trip the GFI cb that is on another circuit. The microwave is new. Any suggestions??????????
Top
Work Gear for Electricians and the Trades
#262 - 01/05/01 07:09 AM Re: SQ. D GFI Circuit Breaker
sparky66wv Offline
Member
Registered: 11/17/00
Posts: 2232
Loc: West Virginia
Don't know if this is any help, but I've been having a tough time even getting SQ D GFCI Circuit Breakers... Something about a recall, I've been told by my local supplier. And I was also told that the problem with them is inadvertant tripping. The symptoms you're having sounds like the problem that started the recall, but I'm really in the dark here and I'm really guessing big time.

Any additional comments, guys?
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Top
#263 - 01/05/01 08:41 AM Re: SQ. D GFI Circuit Breaker
RobertW Offline
Junior Member
Registered: 01/05/01
Posts: 2
Loc: stuart,fl
A micro oven doesnt have to be on a gfci circuit.If you microwave is in the kitchen.it can be pluged in to a dedicated single 20 a recp. the reason your gfi trips on another circuit doesnt make sense.If the micro is pluged in to another one.it is possible you may think its on a diffrent circuit but it could be fed downstream from the gfci breaker or device.
Top
#264 - 01/05/01 03:08 PM Re: SQ. D GFI Circuit Breaker
Bennie R. Palmer Offline
Member
Registered: 11/09/00
Posts: 72
Loc: Milwaukie, OR 97267 USA
Bob: This is an interesting event. There is always a logical explanation for all effects of electricity. Unfortunately, I do not have an immediate answer, or possibly no answer.
I will investigate the power supplies of micro-wave ovens. I think they present a non linear load. This can produce a distorted sine wave. I will also look at frequencies this produces, and see if there can be some relationship with the sensing system of the other non related device.
Keep us informed if you discover a more sensible resolution, or cause.
Top
#265 - 01/05/01 04:55 PM Re: SQ. D GFI Circuit Breaker
jeff1 Offline
Junior Member
Registered: 12/29/00
Posts: 2
Hi,

My 1 & 1/4 cents worth ( darn Canadian money )....most microwaves will operate ok on a 15 amp circuit....but with the power output increasing every year ( 800-900-1000-1100 watts ) it may be best to have a 12 gauge 20 amp circuit dedicated for the micro only.
We have run into this with many of the newist micros on the market. A standard outlet and breaker is often best :-)

jeff.
http://www.applianceaid.com/
Top
#266 - 01/06/01 04:36 AM Re: SQ. D GFI Circuit Breaker
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
I had a situation where a neutral was bad, but it only showed up under a load condition.
I'd be inclined to crank up that wave, and do some metering....
Top
#267 - 02/23/01 11:17 PM Re: SQ. D GFI Circuit Breaker
silverbk Offline
Member
Registered: 02/24/01
Posts: 60
Your problem sounds likeit could be an improper splice. I have seen experienced electricians that do not understand the principal behind a GFCI circuit and splice it incorrectly. It's possible that your ground and neutral are bonded together somewhere in the house. In any event I would suggest getting a shortstop and start looking at your junction boxes.
Top
#268 - 02/26/01 05:48 PM Re: SQ. D GFI Circuit Breaker
elec3 Offline
Junior Member
Registered: 02/26/01
Posts: 1
Loc: Thief River Falls, MN,USA
The mic should be on a dedicated cicurit.But if you wish to GFCI the mic try a type B GFCI
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 53 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals