ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

ECN Shout Chat
Top Posters(30 Days)
Admin 19
Recent Posts
Anyone hiring inspectors?
by HotLine1. 03/27/17 08:03 AM
Old decora style outlets
by Admin. 03/25/17 11:40 AM
ESA Arc flash course
by TheShockDoctors. 03/24/17 10:15 AM
fuse rejectors
by HotLine1. 03/24/17 07:53 AM
Another Forum Update
by Admin. 03/22/17 03:04 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
231,603 Are you busy
166,432 Re: Forum
160,704 Need opinion
Who's Online Now
0 registered members (), 58 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#22181 - 02/20/03 08:01 AM ENT  
tsolanto  Offline
Member
Joined: Sep 2002
Posts: 131
Long Island NY
Is it leagal to use ENT undergroung if it is only used as a sleeve.

I know its against code to bury it, but does'nt only that apply if its a raceway system.

Lets say the underground wiring is XLP-USE direct burial. Using this cable we need no conduit.


Work Gear for Electricians and the Trades

#22182 - 02/20/03 06:21 PM Re: ENT  
WNYJim  Offline
Member
Joined: Jun 2002
Posts: 39
Rochester, NY, USA
Why would you want to use EMT underground?
After a few years (maybe months depending on soil conditions) it will start to rust and there will be sharp edges around the cable just waiting to cut into it.
How about using some PVC instead?


#22183 - 02/20/03 06:27 PM Re: ENT  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
ENT (Electrical Nonmetallic Tubing), not EMT


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#22184 - 02/20/03 08:43 PM Re: ENT  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
See 362.10 for "Uses Permitted" and see the following:

(6) Encased in poured concrete, or embedded in a concrete slab on grade where ENT is placed on sand or approved screenings, provided fittings identified for this purpose are used for connections.

(7) For wet locations indoors as permitted in this section or in a concrete slab on or below grade, with fittings listed for the purpose.


[This message has been edited by Joe Tedesco (edited 02-20-2003).]


Joe Tedesco, NEC Consultant

#22185 - 02/20/03 09:12 PM Re: ENT  
Elzappr  Offline
Member
Joined: Dec 2001
Posts: 270
Oregon
Its not being used as a raceway, its just another type of "fill dirt" eh? I suppose someone could use any sort of non-metallic pipe to act as a sleeve.

Trouble is, how would anyone who dug this up know that it was electrical? It might just look like some burried trash.

300.5 talks about backfill materials and also: "protection shall be provided in the form of..suitable running boards, suitable sleeves, or other approved means." This sounds like approval is needed by your AHJ. Though using plastic conduit would appear to be a suitable "sleeve", it might just pose a hazard for those who don't realize there is live wiring in it...but then again, any "running boards" would be just as misleading. The code doesn't stipulate warning ribbons above underground branch circuits -- just service conductors(300.5(D)(3)). If its residential, and not burried deeper than 12 inches (assuming ,120V and gfci protected), then warning ribbon wouldn't be located above the wiring shallow enough to suitably warn any inadvertant digging up of the wiring. So warning ribbon wouldn't do more than serve as a way to identify the burried "sleeve and wiring" as a potential hazard. I don't think I would be comfortable in calling that shot if I was the AHJ.



Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 14 (0.003s) Memory: 0.7666 MB (Peak: 0.9048 MB) Zlib enabled. Server Time: 2017-03-28 02:26:48 UTC