The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Correct rotation, wrong sequence
by Potseal
Yesterday at 03:14 PM
Industrail Control Panel bonding per 409.108
by sparkyinak
12/09/16 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 9
Potseal 9
sparkyinak 8
Texas_Ranger 7
Who's Online
0 registered (), 8 Guests and 1 Spider online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#216768 - 02/14/16 06:01 PM Verifying bonding conductor resistance
LarryC Offline
Member

Registered: 07/05/04
Posts: 776
Loc: Winchester, NH, US
Folks,

Starting a new job in a facility full of CNC machines. Ongoing issue is the failure of machine electrical components. Several machines came from another facility with clean power and rarely failed. Since arrival, the same machines have suffered multiple failures.

Initial suspect is power quality issues. Power quality studies have been performed on some of the busses in the building. Machines have been relocated within the building. Parts of the building electrical system have been upgraded.

Looking to purchase a power quality analyzer to get an understanding the system existing condition. In addition, I am looking to verify the condition of the bonding and grounding systems.

I am familiar with the ground bond testing systems for plug in equipment, but I am not aware of a system to test the bonding conductors of installed machines. I see standards for telecom and IT systems but nothing for industrial machines.

I think there are two separate issues here. Resistance of the "grounding" network and resistance of the bonding conductors to the grounding network.

Any suggestions?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#216769 - 02/14/16 07:42 PM Re: Verifying bonding conductor resistance [Re: LarryC]
twh Offline
Member

Registered: 03/11/04
Posts: 898
Loc: Regina, Sask.
What kind of failures? What other equipment is in the building, or nearby buildings? I'm thinking about harmonics.

Top
#216770 - 02/14/16 08:54 PM Re: Verifying bonding conductor resistance [Re: LarryC]
LarryC Offline
Member

Registered: 07/05/04
Posts: 776
Loc: Winchester, NH, US
I am aware of servo amp power supplies and servo amps failing. The UPS for the server room also sends high and low input line voltage messages.

The one servo power supply I opened up has a a rectifier module that has a 3 phase input and 2 wire DC output. I assume it is a 6 diode rectifier and that will generate the 5th and 11th harmonics.

I believe there are several things going on concurrently. Excessive harmonics, utility surges and sags, transients both internally and externally generated. No idea yet if there are also redundant N-G connections, poor connections, or a deteriorated ground networks. The building is 100+ years old with multiple additions.

To add to the fun, there multiple types and manufacturers of each type of machine.

Top
#216771 - 02/15/16 03:55 AM Re: Verifying bonding conductor resistance [Re: LarryC]
geoff in UK Offline
Member

Registered: 12/30/02
Posts: 172
Loc: UK
For an example of bonding tester google "Megger BT51"

Top
#216772 - 02/15/16 10:08 AM Re: Verifying bonding conductor resistance [Re: geoff in UK]
LarryC Offline
Member

Registered: 07/05/04
Posts: 776
Loc: Winchester, NH, US
Thanks Geoff.

Top
#216773 - 02/15/16 11:36 AM Re: Verifying bonding conductor resistance [Re: LarryC]
twh Offline
Member

Registered: 03/11/04
Posts: 898
Loc: Regina, Sask.
Harmonic currents find their way to capacitors and can damage devices that are between the source and the capacitor or even the capacitor.