The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
breaker meltdown
by sparky
Today at 07:30 PM
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 14
sparky 10
sparky66wv 8
gfretwell 8
Vlado 6
Who's Online
0 registered (), 259 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#215683 - 07/01/15 09:57 AM Some transformers work fine when powered from sec
LarryC Offline
Member

Registered: 07/05/04
Posts: 775
Loc: Winchester, NH, US
Why do some transformers work just fine when powered from the secondary and other don't?

I was using a small (500VA) 240 to 120 step down transformer as a step up for a small load, and I could only get 200V when powering the 120V winding with 120V.

Top
#215684 - 07/01/15 10:56 AM Re: Some transformers work fine when powered from sec [Re: LarryC]
ghost307 Offline
Member

Registered: 05/09/05
Posts: 876
Loc: Chicago Illinois USA
The turns ratio is calculated to account for the losses inherent in the transformation.
Instead of adding more power to compensate for the 240 to 120 losses...you may be deducting twice that value when going from 120 to 240.

The effect is much less noticeable in large transformers so you may not notice it in those cases.
_________________________
Ghost307

Top
#215685 - 07/01/15 09:45 PM Re: Some transformers work fine when powered from sec [Re: LarryC]
JoeTestingEngr Offline
Member

Registered: 11/04/05
Posts: 786
Loc: Chicago, Il.
Larry, are you saying that the unloaded voltage was only 200VAC? Did you verify it by driving the primary at 240VAC? I've driven quite a few backwards and everything followed the turns ratio.

Top
#215686 - 07/02/15 12:55 AM Re: Some transformers work fine when powered from sec [Re: LarryC]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
I wonder if it was really 208-120.
_________________________
Greg Fretwell

Top
#215692 - 07/02/15 03:13 PM Re: Some transformers work fine when powered from sec [Re: gfretwell]
LarryC Offline
Member

Registered: 07/05/04
Posts: 775
Loc: Winchester, NH, US
It really is a 240 to 120 transformer. I checked it with 240 Input and I got 120 Out. I was told this specific transformer is a cheap design. Low power, 50/60 Hz operation.

I have been told that there is now a new(?) rating on other larger dry transformers stating that it is suitable for reverse operation.

I am no longer at that facility to get manufacturer and model numbers.

Top
#215699 - 07/02/15 08:37 PM Re: Some transformers work fine when powered from sec [Re: LarryC]
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
450.11(B) of the 2014 NEC has language about feeding the secondary of a transformer.

Winchester Speedpark is up there in NH. Nice place...had lots of fun there.

Top
#215703 - 07/03/15 08:41 PM Re: Some transformers work fine when powered from sec [Re: shortcircuit]
LarryC Offline
Member

Registered: 07/05/04
Posts: 775
Loc: Winchester, NH, US
Just down the road a couple of miles. Some nights we can just barely hear the cars.