#215683 - 07/01/15 09:57 AM Some transformers work fine when powered from sec
LarryC Offline
Member
Registered: 07/05/04
Posts: 782
Loc: Winchester, NH, US
Why do some transformers work just fine when powered from the secondary and other don't?

I was using a small (500VA) 240 to 120 step down transformer as a step up for a small load, and I could only get 200V when powering the 120V winding with 120V.
Top
Tools for Electricians:
#215684 - 07/01/15 10:56 AM Re: Some transformers work fine when powered from sec [Re: LarryC]
ghost307 Offline
Member
Registered: 05/09/05
Posts: 897
Loc: Chicago Illinois USA
The turns ratio is calculated to account for the losses inherent in the transformation.
Instead of adding more power to compensate for the 240 to 120 losses...you may be deducting twice that value when going from 120 to 240.

The effect is much less noticeable in large transformers so you may not notice it in those cases.
_________________________
Ghost307
Top
#215685 - 07/01/15 09:45 PM Re: Some transformers work fine when powered from sec [Re: LarryC]
JoeTestingEngr Offline
Member
Registered: 11/04/05
Posts: 786
Loc: Chicago, Il.
Larry, are you saying that the unloaded voltage was only 200VAC? Did you verify it by driving the primary at 240VAC? I've driven quite a few backwards and everything followed the turns ratio.
Top
#215686 - 07/02/15 12:55 AM Re: Some transformers work fine when powered from sec [Re: LarryC]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
I wonder if it was really 208-120.
_________________________
Greg Fretwell
Top
#215692 - 07/02/15 03:13 PM Re: Some transformers work fine when powered from sec [Re: gfretwell]
LarryC Offline
Member
Registered: 07/05/04
Posts: 782
Loc: Winchester, NH, US
It really is a 240 to 120 transformer. I checked it with 240 Input and I got 120 Out. I was told this specific transformer is a cheap design. Low power, 50/60 Hz operation.

I have been told that there is now a new(?) rating on other larger dry transformers stating that it is suitable for reverse operation.

I am no longer at that facility to get manufacturer and model numbers.
Top
#215699 - 07/02/15 08:37 PM Re: Some transformers work fine when powered from sec [Re: LarryC]
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
450.11(B) of the 2014 NEC has language about feeding the secondary of a transformer.

Winchester Speedpark is up there in NH. Nice place...had lots of fun there.
Top
#215703 - 07/03/15 08:41 PM Re: Some transformers work fine when powered from sec [Re: shortcircuit]
LarryC Offline
Member
Registered: 07/05/04
Posts: 782
Loc: Winchester, NH, US
Just down the road a couple of miles. Some nights we can just barely hear the cars.
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
01/23/17 12:27 AM
License exam
by TRUE POWER
01/22/17 11:33 PM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
2 registered (Admin, sparkyinak), 82 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals