#215683 - 07/01/15 09:57 AM Some transformers work fine when powered from sec
LarryC Offline
Member
Registered: 07/05/04
Posts: 780
Loc: Winchester, NH, US
Why do some transformers work just fine when powered from the secondary and other don't?

I was using a small (500VA) 240 to 120 step down transformer as a step up for a small load, and I could only get 200V when powering the 120V winding with 120V.
Top
Tools for Electricians:
#215684 - 07/01/15 10:56 AM Re: Some transformers work fine when powered from sec [Re: LarryC]
ghost307 Offline
Member
Registered: 05/09/05
Posts: 899
Loc: Chicago Illinois USA
The turns ratio is calculated to account for the losses inherent in the transformation.
Instead of adding more power to compensate for the 240 to 120 losses...you may be deducting twice that value when going from 120 to 240.

The effect is much less noticeable in large transformers so you may not notice it in those cases.
_________________________
Ghost307
Top
#215685 - 07/01/15 09:45 PM Re: Some transformers work fine when powered from sec [Re: LarryC]
JoeTestingEngr Offline
Member
Registered: 11/04/05
Posts: 781
Loc: Chicago, Il.
Larry, are you saying that the unloaded voltage was only 200VAC? Did you verify it by driving the primary at 240VAC? I've driven quite a few backwards and everything followed the turns ratio.
Top
#215686 - 07/02/15 12:55 AM Re: Some transformers work fine when powered from sec [Re: LarryC]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
I wonder if it was really 208-120.
_________________________
Greg Fretwell
Top
#215692 - 07/02/15 03:13 PM Re: Some transformers work fine when powered from sec [Re: gfretwell]
LarryC Offline
Member
Registered: 07/05/04
Posts: 780
Loc: Winchester, NH, US
It really is a 240 to 120 transformer. I checked it with 240 Input and I got 120 Out. I was told this specific transformer is a cheap design. Low power, 50/60 Hz operation.

I have been told that there is now a new(?) rating on other larger dry transformers stating that it is suitable for reverse operation.

I am no longer at that facility to get manufacturer and model numbers.
Top
#215699 - 07/02/15 08:37 PM Re: Some transformers work fine when powered from sec [Re: LarryC]
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
450.11(B) of the 2014 NEC has language about feeding the secondary of a transformer.

Winchester Speedpark is up there in NH. Nice place...had lots of fun there.
Top
#215703 - 07/03/15 08:41 PM Re: Some transformers work fine when powered from sec [Re: shortcircuit]
LarryC Offline
Member
Registered: 07/05/04
Posts: 780
Loc: Winchester, NH, US
Just down the road a couple of miles. Some nights we can just barely hear the cars.
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 44 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals