The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by Webmaster
01/18/17 12:03 AM
Re: Fabricating Guards out of Lexan?
by frank
01/17/17 04:11 PM
Would ELV branch circuits be a good idea?
by gfretwell
01/17/17 01:26 PM
Why cables look like they do
by Texas_Ranger
01/17/17 12:33 PM
100% breakers?
by Texas_Ranger
01/16/17 06:13 AM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Webmaster 20
HotLine1 19
gfretwell 13
ghost307 12
Trumpy 12
Who's Online
1 registered (Webmaster), 0 Guests and 73 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#214327 - 11/16/14 10:45 AM NM Cable entering boxes.
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
The question came to me about how far must the NM cable sheath enter the boxes? I could only find the information located in 334.15(C). Nothing about entering the box sans the conduit. My answer would be, the sheath must extend beyond the clamping device be it a non-metallic box or a metal one. The person calling me was concerned because his boss wants the sheath to be at least 3/4" into the box.
There's got to be more important things than this dispute.
_________________________
George Little

Top
2017 / 2014 NEC & Related Books and Study Guides
#214329 - 11/16/14 04:32 PM Re: NM Cable entering boxes. [Re: George Little]
HotLine1 Offline


Member

Registered: 04/03/02
Posts: 6829
Loc: Brick, NJ USA
George:
From 314.17 (C) of 2014 NEC.....

Where nonmetallic sheathed cable or multi-conductor Type UF cable is used, the sheath shall extend not less than 6 mm (1/4 in.) inside the box and beyond any cable clamp. In all instances, all permitted wiring methods shall be secured to the boxes.



Edited by HotLine1 (11/17/14 07:04 AM)
Edit Reason: Corrected copy booboo
_________________________
John

Top
#214331 - 11/16/14 11:44 PM Re: NM Cable entering boxes. [Re: George Little]
gfretwell Offline


Member

Registered: 07/20/04
Posts: 9062
Loc: Estero,Fl,usa
1/4" in english
_________________________
Greg Fretwell

Top
#214333 - 11/17/14 01:10 PM Re: NM Cable entering boxes. [Re: George Little]
ghost307 Offline
Member

Registered: 05/09/05
Posts: 897
Loc: Chicago Illinois USA
Yep, 1/4" minimum.
_________________________
Ghost307

Top
#214335 - 11/17/14 03:45 PM Re: NM Cable entering boxes. [Re: George Little]
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Thanks Guys. You are the best. I would have expected it to be in Article 334 but it wasn't. HEY Inspectors have every right to be wrong :)) And I'm probably one of the few that would admit it.

That's what this BB is all about.
_________________________
George Little

Top
#214336 - 11/17/14 06:50 PM Re: NM Cable entering boxes. [Re: George Little]
HotLine1 Offline


Member

Registered: 04/03/02
Posts: 6829
Loc: Brick, NJ USA
George:
As I say to some..."I'm human, I do make mistakes too"
_________________________
John

Top
#214339 - 11/17/14 08:20 PM Re: NM Cable entering boxes. [Re: George Little]
gfretwell Offline


Member

Registered: 07/20/04
Posts: 9062
Loc: Estero,Fl,usa
I guess it is because there is more than one kind of cable and they were trying to avoid the mess that was created when they put a cable rule in 320 and referred to it in all the other cable articles. (like accessible attics in 330.23 334.23 etc)
_________________________
Greg Fretwell