The question came to me about how far must the NM cable sheath enter the boxes? I could only find the information located in 334.15(C). Nothing about entering the box sans the conduit. My answer would be, the sheath must extend beyond the clamping device be it a non-metallic box or a metal one. The person calling me was concerned because his boss wants the sheath to be at least 3/4" into the box.
There's got to be more important things than this dispute.
_________________________
George Little
Top
2017 / 2014 NEC & Related Books and Study Guides
#214329 - 11/16/14 04:32 PM Re: NM Cable entering boxes. [Re: George Little]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
George:
From 314.17 (C) of 2014 NEC.....

Where nonmetallic sheathed cable or multi-conductor Type UF cable is used, the sheath shall extend not less than 6 mm (1/4 in.) inside the box and beyond any cable clamp. In all instances, all permitted wiring methods shall be secured to the boxes.



Edited by HotLine1 (11/17/14 07:04 AM)
Edit Reason: Corrected copy booboo
_________________________
John
Top
#214331 - 11/16/14 11:44 PM Re: NM Cable entering boxes. [Re: George Little]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
1/4" in english
_________________________
Greg Fretwell
Top
#214333 - 11/17/14 01:10 PM Re: NM Cable entering boxes. [Re: George Little]
ghost307 Offline
Member
Registered: 05/09/05
Posts: 900
Loc: Chicago Illinois USA
Yep, 1/4" minimum.
_________________________
Ghost307
Top
#214335 - 11/17/14 03:45 PM Re: NM Cable entering boxes. [Re: George Little]
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Thanks Guys. You are the best. I would have expected it to be in Article 334 but it wasn't. HEY Inspectors have every right to be wrong :)) And I'm probably one of the few that would admit it.

That's what this BB is all about.
_________________________
George Little
Top
#214336 - 11/17/14 06:50 PM Re: NM Cable entering boxes. [Re: George Little]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
George:
As I say to some..."I'm human, I do make mistakes too"
_________________________
John
Top
#214339 - 11/17/14 08:20 PM Re: NM Cable entering boxes. [Re: George Little]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I guess it is because there is more than one kind of cable and they were trying to avoid the mess that was created when they put a cable rule in 320 and referred to it in all the other cable articles. (like accessible attics in 330.23 334.23 etc)
_________________________
Greg Fretwell
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 81 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals