#208721 - 02/07/13 09:42 PM Outdoor Patio Heating & Residential Load Calcs
BigB Offline
Member
Registered: 03/31/04
Posts: 719
Loc: Tucson, AZ USA
I am pretty sure infrared heaters installed on outdoor patios must be figured at 125% and included on residential load calcs, is this correct?
Top
2017 / 2014 NEC & Related Books and Study Guides
#208722 - 02/07/13 11:27 PM Re: Outdoor Patio Heating & Residential Load Calcs [Re: BigB]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
They get computed at 100% on the load calc but the branch circuit gets sized at 125%.
_________________________
Greg Fretwell
Top
#208726 - 02/08/13 07:22 AM Re: Outdoor Patio Heating & Residential Load Calcs [Re: gfretwell]
BigB Offline
Member
Registered: 03/31/04
Posts: 719
Loc: Tucson, AZ USA
OK thanks Greg
Top
#208728 - 02/08/13 11:03 AM Re: Outdoor Patio Heating & Residential Load Calcs [Re: BigB]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Depending on which method you use the bottom line may not end up being the whole load added with the heaters but the 100% is what you plug into the calculation.
_________________________
Greg Fretwell
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 48 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals