Outdoor Patio Heating & Residential Load Calcs
-
02/08/13
05:42 AM
I am pretty sure infrared heaters installed on outdoor patios must be figured at 125% and included on residential load calcs, is this correct?
Posted By:
gfretwell
Re: Outdoor Patio Heating & Residential Load Calcs
-
02/08/13
07:27 AM
They get computed at 100% on the load calc but the branch circuit gets sized at 125%.
Posted By:
BigB
Re: Outdoor Patio Heating & Residential Load Calcs
-
02/08/13
03:22 PM
OK thanks Greg
Posted By:
gfretwell
Re: Outdoor Patio Heating & Residential Load Calcs
-
02/08/13
07:03 PM
Depending on which method you use the bottom line may not end up being the whole load added with the heaters but the 100% is what you plug into the calculation.
©