The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Temporarily feeding a panel...
by Potseal
09/29/16 01:29 PM
Locked rotor, no burnout
by jraef
09/29/16 01:18 PM
Massive power outage South Australia
by Meadow
09/29/16 06:46 AM
short circuit??
by Meadow
09/29/16 06:43 AM
Norwegian power?
by Meadow
09/29/16 06:36 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 13
sparky 10
sparky66wv 8
gfretwell 8
Vlado 6
Who's Online
3 registered (Potseal, gfretwell, jraef), 103 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#206016 - 05/10/12 09:16 AM Main lug panels
sparkync Offline
Member

Registered: 10/17/02
Posts: 811
Loc: NC
Wonder if someone can refresh me on the code for main lug only panels? As long as I have a Main breaker in the "Service Equipment" outside at the meter, can I use a Main lug panel for the interior panel?? Thanks, Steve

Top
2014 / 2011 NEC & Related Books and Study Guides
#206017 - 05/10/12 11:08 AM Re: Main lug panels [Re: sparkync]
gfretwell Online   content

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
The short answer is yes you can use a MLO if the disconnect is inside or outside the building served. 225.32 & 230.71(A)(1)

There used to be an extra fly in the pudding when we had "lighting and appliance" panelboards but that went away a cycle ago.
_________________________
Greg Fretwell

Top
#206018 - 05/10/12 11:15 AM Re: Main lug panels [Re: gfretwell]
sparkync Offline
Member

Registered: 10/17/02
Posts: 811
Loc: NC
Thanks Greg. That's what I thought, but didn't remember the code reference. For the homeowner's convenience, I usually go ahead and install one with a main breaker anyway, but on a job I'm fixing to do, the main lug panel will probably be better, and always a little cheaper:)