#205697 - 03/22/12 08:14 PM Inspector disapproval the Poggenphol kitchen light
yan Offline
New Member
Registered: 03/22/12
Posts: 1
Loc: Michigan, USA
Hi, I am new to this forum and need your big help,

I have bought a Poggenphol kitchen, see the attached picture. The city electrial inspector disapproval of the kitchen:
1. Need UL listing for the kicthen canbinet becasue the backsplash is lighted,see the picture in this link: http://www.architonic.com/pmgal/plusmodo-poggenpohl/1141490
2. need plugs every 4 feet, but this kitchen is already built and the backsplash is the glass box;
3. the lights and the plug can not be in same circuit, but this is already made this way by PoggenPhol company.
Thanks for all of your inputs,
Yan
Top
Building Codes & Related References
#205698 - 03/22/12 08:24 PM Re: Inspector disapproval the Poggenphol kitchen light [Re: yan]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
I am not sure the inspector has any choice. That is what the code says.
My major concerns would be the light on the receptacle circuits, how many 20a receptacle circuits you have and whether the receptacles meet the spacing requirements. If it was compliant on those points I might give you a break on the listing, assuming it looked safe.

It is too bad that PlusMudo did not sell you a compliant product. It does look nice.
I would get the factory rep to tell you what they are going to do for you.
_________________________
Greg Fretwell
Top
#205700 - 03/22/12 09:25 PM Re: Inspector disapproval the Poggenphol kitchen light [Re: yan]
pdh Offline
Member
Registered: 01/20/05
Posts: 354
Are they selling this in the USA, or did you order it from overseas? if in the USA, they do need to get in compliance with the codes here.

I don't know what's up with UL listings for cabinets, as lots of homes physically construct them as custom during build or remodel. But if the lights underneath get hot, I certainly am concerned. But UL is not doable on custom construction.

They do need to have the outlets every 4 feet. That isn't hard to do.

I do know that aftermarket undercabinet lights do get plugged into the countertop outlets.

I do wonder what inspectors might do for cases where a house is being built with the intent to install attached furnishings that fully cover the walls with built-in lights and outlets that meet code. WHen unattached furniture blocks an outlet, that seems to be OK (even though I think it is bad). But what about attached stuff that will be semi-permanent. The inspector can walk into a kitchen under construction and see NO outlets in the usual places. Plans call for that furnishing to be installed that will make for the right outlets. But that's installed later when other stuff like drywall is done.
Top
#205704 - 03/23/12 12:56 AM Re: Inspector disapproval the Poggenphol kitchen light [Re: yan]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
I was assuming this assembly got hardwired into the rough. If it is actually cord and plug connected it brings up more questions.
_________________________
Greg Fretwell
Top
#205705 - 03/23/12 06:31 AM Re: Inspector disapproval the Poggenphol kitchen light [Re: yan]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6775
Loc: Brick, NJ USA
A custom, high end contractor has a similar unit to the 'Sargento' wall unit with the built-in appliances; it is an imported item, I believe from Italy. It was installed 'to 2008 NEC' requirements. Three (3) 120/20 countertop circuits, etc.

The 'rough' for the required circuits and spacing issues was achieved via a nice plugmold install. The lighting circuits were also field wired, luminaires came with cabinets; UL/TUV labels.

Looking briefly thru the linked site...seems to be all european goods; I did not see any reference to any listings.

As to cabinets with UL labels? I never gave that a thought, although we do check all electrical devices.
_________________________
John
Top
#205832 - 04/09/12 10:51 PM Re: Inspector disapproval the Poggenphol kitchen light [Re: HotLine1]
BigB Offline
Member
Registered: 03/31/04
Posts: 719
Loc: Tucson, AZ USA
Originally Posted By HotLine1


As to cabinets with UL labels? I never gave that a thought, although we do check all electrical devices.


The cabinet contains built in lighting, wouldn't that require a listing?
Top
#205834 - 04/10/12 12:12 AM Re: Inspector disapproval the Poggenphol kitchen light [Re: yan]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
I would look for a listing mark on the luminaire but I don't think the whole cabinet needs a listing.
_________________________
Greg Fretwell
Top
#205840 - 04/10/12 06:15 PM Re: Inspector disapproval the Poggenphol kitchen light [Re: yan]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6775
Loc: Brick, NJ USA
Greg:
Have you ever seen a UL/other label on any kitchen cabinets?
_________________________
John
Top
#205846 - 04/10/12 11:20 PM Re: Inspector disapproval the Poggenphol kitchen light [Re: yan]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
No that is why I sad that.
I have seen U/L listings on office cabinet assemblies tho. (components of wired cubicle systems)
I suppose there might be an AHJ somewhere who would draw this parallel in a modular kitchen system with internal wiring.
_________________________
Greg Fretwell
Top
#206425 - 07/01/12 10:29 AM Re: Inspector disapproval the Poggenphol kitchen light [Re: yan]
harold endean Offline
Member
Registered: 02/16/02
Posts: 2233
Loc: Boonton, NJ
Can they get a field certification from a listing agency?
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 61 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals