#203186 - 09/13/11 05:32 PM phase converter problems?
watthead Offline
Member
Registered: 10/13/01
Posts: 172
Loc: South Carolina
I need an expert or someone with a working knowledge of phase generators. I have phase convertor that runs a small piece of equipment with 3 three phase motors. The problem is a 5hp fan motor is going out on overload. I believe the problem is in the convertor but I am not sure. The single phase 240v supply to the convertor is good. The no load voltages at the convertor are A=122v B=122V C=196v AB=244v BC=210v AC=206v. The currents at the 5hp fan motor are A=2.9 B=20.2 C=13.1 under this load the voltages are AB=240 BC=196 AC=206 Anyone have any ideas or suggestions to determine the actual problem. They would be more than welcomed
Top
Work Gear for Electricians and the Trades
#203188 - 09/13/11 08:46 PM Re: phase converter problems? [Re: watthead]
JoeTestingEngr Offline
Member
Registered: 11/04/05
Posts: 781
Loc: Chicago, Il.
You should probably supply info on the type of converter that you are using.
Joe
Top
#203189 - 09/13/11 09:38 PM Re: phase converter problems? [Re: watthead]
watthead Offline
Member
Registered: 10/13/01
Posts: 172
Loc: South Carolina
it is a rotary converter that has been in service for a couple of years.
Top
#203190 - 09/13/11 10:21 PM Re: phase converter problems? [Re: watthead]
LarryC Offline
Member
Registered: 07/05/04
Posts: 780
Loc: Winchester, NH, US
When you open up the converter, it has a bunch of canned power capacitors, correct? If so, my GUESS is that you have some bad capacitors. Look for the ones that are swelled or really hot.

Did you have some recent power outages or local lightning strikes? Those caps are AC rated electrolytics. Make sure if they need to be replaced, that you pay attention to the voltage ratings. If I remember right, they were typically rated for 600 VAC.
Top
#203191 - 09/13/11 10:53 PM Re: phase converter problems? [Re: watthead]
watthead Offline
Member
Registered: 10/13/01
Posts: 172
Loc: South Carolina
Yes there are capacitors inside the starter enclosure. I will check those , thanks.
Top
#203212 - 09/14/11 04:32 PM Re: phase converter problems? [Re: watthead]
watthead Offline
Member
Registered: 10/13/01
Posts: 172
Loc: South Carolina
Thanks Larry, it was the capacitors. Both run capacitors were bad and when replaced the B phase current fell drastically.
Top
#203218 - 09/14/11 08:50 PM Re: phase converter problems? [Re: watthead]
Tesla Offline
Member
Registered: 06/16/04
Posts: 1273
Loc: Sacramento, CA
Not withstanding their higher price -- you're better off with Run Caps...

They're made to MUCH higher standards.
_________________________
Tesla
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6775
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 14 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals