I need an expert or someone with a working knowledge of phase generators. I have phase convertor that runs a small piece of equipment with 3 three phase motors. The problem is a 5hp fan motor is going out on overload. I believe the problem is in the convertor but I am not sure. The single phase 240v supply to the convertor is good. The no load voltages at the convertor are A=122v B=122V C=196v AB=244v BC=210v AC=206v. The currents at the 5hp fan motor are A=2.9 B=20.2 C=13.1 under this load the voltages are AB=240 BC=196 AC=206 Anyone have any ideas or suggestions to determine the actual problem. They would be more than welcomed