The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
1 registered (gfretwell), 218 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#20136 - 01/09/03 06:32 AM Padlock on Service Disconnect
Frank Cinker Offline
Member

Registered: 07/29/01
Posts: 317
Loc: Pennsylvania
Is it ever legal to padlock a service disconnect in the "on" position? I reviewed Article 230 and could not find an exception. I personally don't think it's legal. The problem is every so often a mischievous person will turn the main switch off at one of our public facilities. The switch is located outdoors to public access. Is there any accepted practice to solve such a problem.

Frank

[This message has been edited by Frank Cinker (edited 01-09-2003).]

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#20137 - 01/09/03 06:36 AM Re: Padlock on Service Disconnect
C-H Offline

Member

Registered: 09/17/02
Posts: 1508
Loc: Stockholm, Sweden
Put a camera above the disco that takes a snapshot when the disco is operated.

Top
#20138 - 01/09/03 06:47 AM Re: Padlock on Service Disconnect
Wirenuttt Offline
Member

Registered: 11/10/02
Posts: 267
Loc: Massachusetts
That's a real p.i.t.a.. Camera seems like a good solution. Locking it could be a problem in emergency situations. Wondering if the AHJ and fire dept. would allow a lock box mounted next to the disco with a key to the pad lock like they use for fire alarm. The F.D. carries the key to the lock box. I beleive it's a standard key to fit all lock boxs in that same city.Might be worth asking the ahj and f.d. to find out. Tell them the situation your in. Hope this helps.
~Ange

Top
#20139 - 01/09/03 07:17 AM Re: Padlock on Service Disconnect
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
I think the camera's a good idea. I think a lock on the disco's not. (240.24?) A frangible lock might be OK, but it's as easy for a vandal to break it as the FD.
Put one up in an obvious position, and have another that's hidden.
Scott 35, the "Bank Man", is probably the best guy to answer this Q.
Hey, Scott, you around?


[This message has been edited by electure (edited 01-09-2003).]

Top
#20140 - 01/09/03 07:32 AM Re: Padlock on Service Disconnect
Creighton Offline
Member

Registered: 01/06/02
Posts: 56
Loc: Hayward, CA
230.70(A)(1) only requires that the disconnect LOCATION be readilly accessible. Where accessible to the public it is logical to lock the disconnect to avoid vandalism. Most commercial buildings have the service equipment in a locked room. Nothing wrong with that. 230.92 recognizes that the service disconect may be locked.

Top
#20141 - 01/09/03 07:41 AM Re: Padlock on Service Disconnect
Creighton Offline
Member

Registered: 01/06/02
Posts: 56
Loc: Hayward, CA
Forgot to mention that even with the switch handle locked, or the circuit breaker handle locked on, the fuses will still blow, and the circuit breaker being trip-free will open, so there is little sacrifice of safety involved.

Top
#20142 - 01/09/03 09:51 AM Re: Padlock on Service Disconnect
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
These days, there are cases where absence of power creates a greater hazard, such as loss of area lighting. A trade magazine in the eighties discussed litigation involving a disconnect switch serving a bilge pump that was turned off by a vandal, causing flooding and significant property damage.

Some externally operable switches have an index mark on the handle flange/lockplate for field drilling a shackle hole for “on” padlocking.

http://www.squared.com/us/products/s ...0BR9801R601.pdf page 5/item 22—The switch can also be modified so that the switch can be locked in the ON position if required by the application.




[This message has been edited by Bjarney (edited 01-09-2003).]

Top
#20143 - 01/09/03 10:21 AM Re: Padlock on Service Disconnect
Frank Cinker Offline
Member

Registered: 07/29/01
Posts: 317
Loc: Pennsylvania
It seems as if the AHJ rules absence of power creates a greater hazard a service disconnect can be locked in the on position. Just the fact some Square D disconnects have provisions for such a padlock installation makes me believe it could be legal. I plan to call our Public Safety Department tomorrow morning to get a ruling.
Thank you for the excellent information.

Top
#20144 - 01/09/03 03:37 PM Re: Padlock on Service Disconnect
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Frank:
Have had the same situation a few times here in NJ.
OK to lock on with a "breakaway Padlock".
Same type used on exterior sprinkler system valves.
Yes, this is a PITA.
Your local AHJ should not have a problem.
As stated above OCP will still function, and in an emergency, the breakaway lock is acceptable.
John
_________________________
John

Top
#20145 - 01/10/03 04:52 AM Re: Padlock on Service Disconnect
Frank Cinker Offline
Member

Registered: 07/29/01
Posts: 317
Loc: Pennsylvania
I am not familiar with a breakaway padlock. Is there a product website I can look at?
I assume it looks like a standard padlock.

Frank

Top