#200384 - 03/29/11 07:24 PM 6 cct on contactor
Joetools Offline
New Member
Registered: 02/02/10
Posts: 9
Loc: Alberta
looking to put 6 ccts (lighting) on a contactor controlled by a time clock. I'm kinda new, and not sure how to go about it. are there 6 pole contactors?
Top
Work Gear for Electricians and the Trades
#200385 - 03/29/11 07:33 PM Re: 6 cct on contactor [Re: Joetools]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
Two 3 pole contactors is probably cheaper than a 6 pole, if you could find one. Try GE CR206L20GAZZ
_________________________
Greg Fretwell
Top
#200388 - 03/29/11 10:25 PM Re: 6 cct on contactor [Re: Joetools]
twh Offline
Member
Registered: 03/11/04
Posts: 899
Loc: Regina, Sask.
Check 30-710(4) for the rating of the contactor. Appendix B refers to CSA C22.2 #14, which means nothing to me, but it might allow for a lower rating if the contactor is rated in HP. The rule is that for HID lighting, the rating must be double the ampere load.
Top
#200389 - 03/30/11 05:19 AM Re: 6 cct on contactor [Re: Joetools]
ghost307 Offline
Member
Registered: 05/09/05
Posts: 897
Loc: Chicago Illinois USA
ASCO makes lighting contactors with as many poles as you need. A mere 6 poles should be no problem at all.

http://www.emersonnetworkpower.com/en-US...chCircuits.aspx
_________________________
Ghost307
Top
#200391 - 03/30/11 06:03 AM Re: 6 cct on contactor [Re: Joetools]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Please note that lighting loads should use contactors described as 'lighting contactors,' rather than the less robust 'definite purpose contactors.'
Top
#200405 - 03/30/11 10:09 PM Re: 6 cct on contactor [Re: Joetools]
Joetools Offline
New Member
Registered: 02/02/10
Posts: 9
Loc: Alberta
thanks! 2 - 3pole contactors will work. Now, installing the time clock. There are 4 terminals, 2 line, 2 load. I'll parallel up the coils, but I don't see where I would need 2 wires in and 2 out for the time clock. I seem to remember there being a removable bridge in the time clock. Do I just remove this to have the 2 lines in so it acts like a switch for the contactors? But it must need power all the time to function, so ...... where does that come from? the contactors are the load side?

advice much appreciated!
Top
#200407 - 03/31/11 12:23 AM Re: 6 cct on contactor [Re: Joetools]
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8560
Loc: SI,New Zealand
Originally Posted By Joetools
thanks! 2 - 3pole contactors will work. Now, installing the time clock. There are 4 terminals, 2 line, 2 load. I'll parallel up the coils, but I don't see where I would need 2 wires in and 2 out for the time clock. I seem to remember there being a removable bridge in the time clock. Do I just remove this to have the 2 lines in so it acts like a switch for the contactors? But it must need power all the time to function, so ...... where does that come from? the contactors are the load side?

Joe,
The feed phase wire from the supply would go to one of the Line terminals, the other Line terminal will be for the neutral, this will often have a link between the line and load side of the time switch, use a meter to confirm this though.
Connect your contactors to the Load side of the time switch.

Hope this helps.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
#200499 - 04/04/11 04:24 AM Re: 6 cct on contactor [Re: Joetools]
pooL8 Offline
Member
Registered: 02/18/11
Posts: 56
Loc: BC Canada
1 Pole
2 Pole
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
0 registered (), 66 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals