The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
Yesterday at 09:33 AM
breaker meltdown
by crselectric
Yesterday at 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm≤ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 17
gfretwell 9
sparky 9
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 284 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#196980 - 11/03/10 02:29 PM Mixed cables and conductors in a raceway?
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
Is there a violation if you used a cable with another conductor or two in a raceway system?
(example a 12-3 w/g Romex and an additional THHN for the 4th ungrounded conductor in a 3/4" raceway).
It didn't sound right when I heard it but I am not sure what you would cite.
_________________________
Greg Fretwell

Top
2014 / 2011 NEC & Related Books and Study Guides
#196981 - 11/03/10 05:00 PM Re: Mixed cables and conductors in a raceway? [Re: gfretwell]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6785
Loc: Brick, NJ USA
That's interesting...
I must say none of the rocket scientists here thought that up....yet!
Time to ponder what (if anything) to cite.

FYI: another reason to add common sense to the NEC?
_________________________
John

Top
#196982 - 11/03/10 05:34 PM Re: Mixed cables and conductors in a raceway? [Re: gfretwell]
Niko Offline
Member

Registered: 08/17/06
Posts: 358
Loc: Campbell, CA
can you install NM cable in a complete raceway system? Or only in a piece of raceway just for physical protection?
_________________________
Be kind to your neighbor, he knows where you live


Top
#196987 - 11/03/10 06:58 PM Re: Mixed cables and conductors in a raceway? [Re: Niko]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
I can't cite any rule that says you can't have NM cable in a raceway system. Since all circuit conductors come through the same connector there are no inductive heating problems. I know this is ugly but I am stumped to come up with a violation.
_________________________
Greg Fretwell

Top
#196994 - 11/04/10 11:37 AM Re: Mixed cables and conductors in a raceway? [Re: gfretwell]
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
It's not a violation.

However, due to economics you'd not expect to see it.

It's generally impractical.
_________________________
Tesla

Top
#196996 - 11/04/10 12:09 PM Re: Mixed cables and conductors in a raceway? [Re: Tesla]
KJay Offline
Member

Registered: 11/27/07
Posts: 763
Loc: MA, USA
Iím wondering if 300.3[B] and 300.3[B],1 might apply if the conductors are all part of the same circuit, since both also state the same "cable or cord" as well.
Something else maybe, is that 334.15[B] is for exposed work, so not sure if this would preclude the NM from being run in a conduit that is concealed or partially concealed.

Top
#197000 - 11/04/10 03:26 PM Re: Mixed cables and conductors in a raceway? [Re: KJay]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
I suspect the RX was there first and the THHN was added.

KJay, this was all exposed in a garage/shop. A 240 2 pole was converted to 120/240 3 pole from what I could assume.
I see RX in pipe quite a bit, just because that is what resi guys have on the truck or what homeowners buy at the HD. I bet 99% of it is fed into the pipe as they build the system just because of how hard it is to pull RX in pipe.
I think part of it is you can buy RX cheaper than THHN if you don't want 500 feet.

I was not AHJ, just asked if it was legal as "gee whiz" info.
_________________________
Greg Fretwell

Top
#197002 - 11/04/10 04:28 PM Re: Mixed cables and conductors in a raceway? [Re: gfretwell]
KJay Offline
Member

Registered: 11/27/07
Posts: 763
Loc: MA, USA
I guess technically you might be able to say that EMT fittings are not designed or listed for use with NM cables, since I see where 300.15 says that fittings and connectors shall be used only with the specific wiring method for which they are designed and listed.

IMO, I donít think the NEC allowing NM to be sleeved for protection was intended to allow unlimited use like that, but Iím also not sure exactly where to find a specific rule prohibiting it.

Top
#197004 - 11/04/10 04:46 PM Re: Mixed cables and conductors in a raceway? [Re: KJay]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6785
Loc: Brick, NJ USA
Kjay:
The fittings you reference above are EMT, and used on the EMT, not the NM as I understand Gregs description. 300.15 would be a bad cite.

I tend to say there is nothing to directly cite, unless at the begining of the circuit, there is no 'from-to' connector.
_________________________
John

Top
#197030 - 11/05/10 06:40 PM Re: Mixed cables and conductors in a raceway? [Re: HotLine1]
KJay Offline
Member

Registered: 11/27/07
Posts: 763
Loc: MA, USA
Originally Posted By: HotLine1
Kjay:
The fittings you reference above are EMT, and used on the EMT, not the NM as I understand Gregs description. 300.15 would be a bad cite.

I tend to say there is nothing to directly cite, unless at the begining of the circuit, there is no 'from-to' connector.



True. It was just something to mull over. My thought was that NM is a separate wiring method with its own installation requirements and listed connectors, etc.