"Equipotential grid:" seldom has anything so agitated code issues as much as when this idea was introduced to swimming pools a few cycles back. In 2005 the NEC called for a copper mesh; by 2008 the language had backed off somewhat, to where ordinary steel reinforcing mesh qualified.

The real confusion abounded when the pool deck was something besides concrete; for example, when pavers were set in a bed of sand.

When I did such a pool last year, I went 'beyond' the strict NEC requirements, and actually did use a roll of the copper mesh for the areas adjacent to the pool equipment, and between the pool equipment and the pool itself. My reasoning was that this area was where faults were more likely to develop, and I chose the copper for its' greater corrosion resistance.

That single roll of mesh (3' x 50'), and the associated split-bolt connectors, cost about $850. Net. My cost. It covered about 1/4 of the pool perimeter.

According to the latest IAEI update, this part of the code has been the subject of much discussion by the 2011 panel. It seems that ONE inspector, backed by ONE manufacturer, has instituted some manner of 'appeal' to get the copper mesh requirement included in the 2011 NEC.

This 'appeal' process is a new twist to me! Proposal, committee, vote ... then local adoption / ammendment .... I thought that's how the NEC was made - not by endless litigation funded by deep pockets.

What are your thoughts?
Top
2017 / 2014 NEC & Related Books and Study Guides
#195358 - 07/28/10 09:45 PM Re: Pool Grid: Revisited [Re: renosteinke]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6833
Loc: Brick, NJ USA
Reno:

Want a laugh?

How about a 680.26 grid required on a wooden deck for a hot tub install!

Seriously, that is a story going around with some ECs as an opinion from a code specialist!

We had the grid debate here for above ground pools, opinion from State was....grid required...dirt, grass, stones (gravel), pavers, concrete, whatever!

_________________________
John
Top
#195362 - 07/29/10 12:32 AM Re: Pool Grid: Revisited [Re: HotLine1]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
I would say if there was an elevated deck of non-conductive material around the above ground pool, 3 feet out, no grid. If you can stand in the mud and put your hand in the pool, grid. The rule said "paved surface" in 2005, now it just says "perimeter surface" which would include grass/mud.
Reno the grid requirement in concrete was rebar, bonded, just like pool steel or you could use the copper mesh, later (2008) reduced to a single #8 ring.
The reality is, a single #3 rebar looping the pool might be cheaper that the #8 copper. They also removed the word "bar" so, presumably it could be regular "six over" steel mesh.
Ask your AHJ wink
_________________________
Greg Fretwell
Top
#195364 - 07/29/10 04:41 AM Re: Pool Grid: Revisited [Re: gfretwell]
sparky Offline
Member
Registered: 10/18/00
Posts: 5545
most local pool and/or hot tub companies here do the entire install , and then call sparky

i've always been a tad nixed that they get away with doing my job, and have me vouch for it by proxy

let the AHJ's have a word with them i say....

~S~
Top
#195369 - 07/29/10 06:32 AM Re: Pool Grid: Revisited [Re: sparky]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
As I understand it, the specific issue here is not just to have a grid, but to require it to be of copper. The advocate asserts that the single #8 wire that we already have encircling the pool is not adequate.
Top
#195373 - 07/29/10 10:24 AM Re: Pool Grid: Revisited [Re: renosteinke]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
If you are bonding dirt, it has to be copper. If this is encased in concrete it can be the steel rebar or presumably after 2008, steel mesh.

I understand some people do not think a single #8 is sufficient but Florida decided in 2006-7 that this would work and adopted the 2008 rule early as an addendum.
(probably driven by the pool lobby)
I am not sure where any of this actually came from and what testing was done to prove the effectiveness but differences in soil material, moisture content and the surface itself would make this testing somewhat useless when any of those changed from the tested media.
_________________________
Greg Fretwell
Top
#195380 - 07/29/10 05:41 PM Re: Pool Grid: Revisited [Re: gfretwell]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
It HAS to be copper if you're bonding dirt? Where is that derived from? I spent a considerable amopuntof time with out local AHJ before developing my plan, and we all managed to miss that little detail.
Top
#195397 - 07/29/10 08:40 PM Re: Pool Grid: Revisited [Re: renosteinke]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
680.26(B)(2)(b)(1)

You do not structurally reinforce dirt so (a) is out wink

Steel in dirt would be red dust an a year if you live in a place where it rains.
_________________________
Greg Fretwell
Top
#195746 - 08/20/10 06:39 AM Re: Pool Grid: Revisited [Re: gfretwell]
harold endean Offline
Member
Registered: 02/16/02
Posts: 2248
Loc: Boonton, NJ
I have also seen companies that sell rubber mats that go all around the hot tub so that you don't have to use the grounding ring. This comes in handy when you set a tub upon an existing concrete patio.
Top
#195755 - 08/20/10 09:32 AM Re: Pool Grid: Revisited [Re: harold endean]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
There are also wood deck kits that range from pine to teak for people who want a nicer look. I see them at my pool store.
_________________________
Greg Fretwell
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
License exam
by TRUE POWER
01/23/17 09:16 PM
Looking for older post
by sparkyinak
01/23/17 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
1 registered (Admin), 72 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 11/11/05
Posts: 190

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals