#193608 - 04/09/10 06:20 PM Service Rated?
nhsparky Offline
Member
Registered: 04/03/08
Posts: 19
Loc: N.H.
Can anybody explain to me what defines a "service rated" enclosure. I recently purchased a Cutler Hammer disconnect. In the instructions was the statement-If service rated equipment is required, install provided sticker "service rated" on inside of enclosure. They give you the sticker! Just what is the difference and why don't they just install the sticker to begin with. I have asked my sales rep, who has asked his Mfg rep, and nobody seems to know what makes a service rated enclosure beyond the sticker.
Thanks
Dave
Top
Work Gear for Electricians and the Trades
#193609 - 04/09/10 06:51 PM Re: Service Rated? [Re: nhsparky]
TNT_Tim Offline
Member
Registered: 02/21/07
Posts: 12
Loc: Tennessee
The service disconnecting means must be identified as suitable for use as service equipment [230.66]. This means the service disconnecting means is supplied with a main bonding jumper so that a neutral-to-case connection can be made, as required in 250.24(C) and 250.142(A). The service disconnecting means must open all service-entrance conductors from the structure premises wiring [230.70].
Top
#193610 - 04/09/10 06:59 PM Re: Service Rated? [Re: nhsparky]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6833
Loc: Brick, NJ USA
Dave:
Good question. Perhaps, installing the sticker on all discos may be 'mis-leading' IF the disco is not used for 'service'. Giving the option to install it if necessary, also reduces inventory for mfg., suppliers, etc.

Just a guess on my part, perhaps the CH rep may want to adopt it! If he's interested, PM me for where to mail the check. (LOL)

_________________________
John
Top
#193611 - 04/09/10 08:14 PM Re: Service Rated? [Re: HotLine1]
luckyshadow Offline
Member
Registered: 01/04/05
Posts: 305
Loc: Maryland USA
Sounds like a good question for UL !
I would think that to be UL listed those stickers should be applied in the factory.
One could easliy save them and apply them to another non service rated piece of equipment!
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
0 registered (), 105 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals