The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

   
Topic Options
Rate This Topic
#192333 - 02/08/10 02:42 PM Old work grounding stumper
Haligan Offline
Member
Registered: 02/25/04
Posts: 112
Loc: Berkeley, CA USA
The Scene:
Old work bathroom remodel. GC has it down to the studs.
I'm keeping the existing circuit for lights and fan. 12/2 NM, no grounding
I've pulled a homerun 20a for receps.

How to ground the lights and fan?
A. There's a bare 14ga conductor that was bonding all of the old metal boxes. It is clamped with a grounding electrode to the bathroom's water pipe. This wire then continues off to other parts of the house. I could tap into this. But! Code says bonding to water pipe has to be 5' from source. This seems like a 'better than nothing' option. My least favorite so far.

B. Connect to the grounding of the new 20a circuit. This goes back to the panel and straight to the rod. Problem- I scoured the code and couldn't find an allowance for this.

C. Connect a new electrode and ground the lights and fan to the water pipe.

D. Run 12ga grounding wire all the way back to the panel. This is okay code wise, but raises some new issues.

What's best here?
Top
2017 / 2014 NEC & Related Books and Study Guides
#192334 - 02/08/10 04:52 PM Re: Old work grounding stumper [Re: Haligan]
Jim M Offline
Member
Registered: 08/10/01
Posts: 453
Loc: Chestertown, MD, USA
Since you are down to the studs I would think that a new lighting circuit should be run.
Top
#192336 - 02/08/10 05:26 PM Re: Old work grounding stumper [Re: Jim M]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6833
Loc: Brick, NJ USA
I tend to agree with Jim M.
You may want to run your list of options past the local AHJ, as he is the one to accept or reject your choice(s).

_________________________
John
Top
#192337 - 02/08/10 06:51 PM Re: Old work grounding stumper [Re: HotLine1]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
Best practice would be to run a new wire. Your ideas of using the water pipe, even with another rod, won't work unless you bond back to the existing ground electrode system.
You could share the EGC of the new receptacle circuit you have run but you do have to worry about protecting the wire you run. I would ask if your AHJ is OK with just stringing a THHN over to the receptacle box

Quote:
250.120(C) Equipment Grounding Conductors Smaller Than 6 AWG. Equipment grounding conductors smaller than 6 AWG shall be protected from physical damage by a raceway or cable armor except where run in hollow spaces of walls or partitions, where not subject to physical damage, or where protected from physical damage.
_________________________
Greg Fretwell
Top
#192338 - 02/08/10 07:58 PM Re: Old work grounding stumper [Re: gfretwell]
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Guess I'm trying to figure out why anything has to be done with existing. But if you insist on doing something, item D. is the only one that meets code.
_________________________
George Little
Top
#192339 - 02/08/10 08:34 PM Re: Old work grounding stumper [Re: George Little]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
I was just trying to let safety trump a technical violation (extending the EGC from an existing circuit of sufficient size). I would rather have a ground than not.
_________________________
Greg Fretwell
Top
#192340 - 02/08/10 09:38 PM Re: Old work grounding stumper [Re: gfretwell]
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
I guess I agree with you Greg and I would add, another option would be to wire the fan and lights in the bathroom on the new receptacle circuit. As long as he didn't extend to anything beyond the one bathroom, he'd have not only grounding but GFCI protection ta boot.
_________________________
George Little
Top
#192341 - 02/08/10 10:36 PM Re: Old work grounding stumper [Re: George Little]
Haligan Offline
Member
Registered: 02/25/04
Posts: 112
Loc: Berkeley, CA USA
George- I'm liking 210.11(C)3. The lights and the fan sum up to less than 1amp. Plenty of leftover on the 20a dedicated.

Thanks all
Top
#192345 - 02/09/10 07:29 AM Re: Old work grounding stumper [Re: George Little]
Rewire Offline
Member
Registered: 02/23/08
Posts: 167
Loc: Missouri
Originally Posted By George Little
Guess I'm trying to figure out why anything has to be done with existing. But if you insist on doing something, item D. is the only one that meets code.
The only method that would be questionable would be B but all the others are code compliant
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
Today at 02:22 PM
License exam
by TRUE POWER
Yesterday at 09:16 PM
Looking for older post
by sparkyinak
Yesterday at 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
1 registered (Admin), 89 Guests and 15 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/17/06
Posts: 358

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals