The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
breaker meltdown
by sparky
Yesterday at 07:30 PM
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 13
sparky 10
gfretwell 8
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 61 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#185763 - 03/26/09 10:41 AM 250.104(C) Bonding of isolated steel I-beam
earlydean Offline
Member

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
I would like to read about your past practices and experiences with inspectors as regards to bonding of isolated and exposed steel I beams in otherwise wood frame construction. There is no way this steel may become energized, as no electrical item is mounted on it, nor is any wiring method attached to or even resting on it. Is it required to be bonded or not?
_________________________
Earl

Top
2014 / 2011 NEC & Related Books and Study Guides
#185776 - 03/26/09 03:59 PM Re: 250.104(C) Bonding of isolated steel I-beam [Re: earlydean]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Can you give an Example say height , Location , ect.

Top
#185779 - 03/26/09 05:18 PM Re: 250.104(C) Bonding of isolated steel I-beam [Re: Yoopersup]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6785
Loc: Brick, NJ USA
Earl:
Perhaps the steel is mechanically connected to the earth??

In that case....yes...bond
_________________________
John

Top
#185783 - 03/26/09 09:44 PM Re: 250.104(C) Bonding of isolated steel I-beam [Re: HotLine1]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
That is what I usually associate with the beam that goes across the basement. Typically it is an 8x17# on lally columns and caught at each end in a masonry pocket. (up there in the frozen north)
No. I have never seen any serious attempt to bond it.
_________________________
Greg Fretwell

Top
#185790 - 03/27/09 09:32 AM Re: 250.104(C) Bonding of isolated steel I-beam [Re: gfretwell]
JBD Offline
Member

Registered: 07/12/01
Posts: 599
Loc: WI, USA
The NEC says if it is 'likely' to become energized, not if it is just 'possible'.

Should houses along the Gulf coast be built with roofs capable of handling 12" snow loads? Should houses in the far northern Midwest be built to survive hurricanes? Both conditions are possible, however neither is likely. Should nails used to hang pictures be grounded? Aren't they likely to become energized? If they weren't, why the restrictions an how close NM cable can be run near the front of a wall cavity?