The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Today at 08:46 PM
International Wire Colour Codes
by Tjia1981
Yesterday at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 311 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#18015 - 12/05/02 08:27 AM microwave tied in with range
Junior Member

Registered: 10/20/02
Posts: 3
Is it leagle to tap the microwave onto one leg of a 4 wire 40 amp range home run?

The contractor stated 210-19 (c) ex 1 . that it was a cooking unit. The microwave is a 120v unit on a 15 amp rated receptacle.

Any info would be great thanks all
Scott Badger

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#18016 - 12/05/02 10:18 AM Re: microwave tied in with range
mj Offline

Registered: 06/10/02
Posts: 188
Loc: meriidian, ms
what about ocp for the microwave unit ? a 15 unit on a 40 amp circuit? 210-19 (3) this practice is permitted... some electricians use that exception, some dont. take care...

#18017 - 12/05/02 10:57 AM Re: microwave tied in with range
dana1028 Offline

Registered: 01/09/02
Posts: 163
Loc: San Carlos, CA
Is this worked on a permit? Ask the inspector his take on this 'exception'. Most inspectors consider a microwave an appliance and do not allow this exception - microwaves are cord and plug connected and therefore this receptacle could eventually serve other appliances. This 'exception' is a Tap rule...does not apply to receptacles[microwaves are not hardwired]; further your microwave is rated less than 20A. I'd say this is bogus and refuse the installation.

#18018 - 12/05/02 11:24 AM Re: microwave tied in with range
Junior Member

Registered: 10/20/02
Posts: 3
I found out that the microwave was taped into the range feed when I turned off the ranger to make the damn thing stop beeping.(It was the dishwasher that beeped all day lol) MY dad had a good time with that. It make for a fun thanksgiving.

Anways this is a new house. I don't think I will have a problem getting the contractor to fix this. He said he runs a 20A home run to the disposal. That would be a good place to pick up my power for the microwave.
I just wanted to get some feed back from others in the industry.

Thanks again
Scott Badger

#18019 - 12/05/02 05:12 PM Re: microwave tied in with range
Bjarney Offline

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
Under NEC tap rules, could you use a fuseholder receptacle for the microwave oven, if it was furnished with an integral cord?

For example, consider something like a Buss "SRU" described at

#18020 - 12/05/02 06:05 PM Re: microwave tied in with range
electure Offline


Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
Provided there's no range on the circuit
Why not just replace the circuit breaker with a 20 amp back at the panel? Too easy.

#18021 - 12/05/02 06:07 PM Re: microwave tied in with range
spyder Offline

Registered: 10/14/02
Posts: 211
Loc: Massachusetts
I have seem some wall ovens that come with a recptacle in the back to plug the microwave into.

I would not consider the type of tap you are talking about. Run the 12/2 homerun. Many microwaves call for a decicated 20 amp ciruit. Manufacturers specs supersed the code book.