#176922 - 04/16/08 06:56 AM What caused this situation?
Webmaster Offline

Administrator
Member

Registered: 10/07/00
Posts: 3142
Loc: NY, USA
What caused this situation?

submitted by Joe Tedesco:


Top
Tools for Electricians:
#176923 - 04/16/08 07:42 AM Re: What caused this situation? [Re: Webmaster]
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Here's another picture of a situation that is constantly questioned by many everywhere!

The termination's of the EGC and Grounded (Neutral) conductor.

_________________________
Joe Tedesco, NEC Consultant

Top
#176928 - 04/16/08 09:07 AM Re: What caused this situation? [Re: Joe Tedesco]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
(ref top pic)
A loose connection and an uncleared ground fault?
It looks like the bottom conductor wasn't inserted all the way through and missed being clamped by the screw
_________________________
Greg Fretwell

Top
#176933 - 04/16/08 09:27 AM Re: What caused this situation? [Re: gfretwell]
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
The panel EGC and neutral look awfully small... And the terminal bus is rusty.

Looks also like the insulation wasn't stripped properly on that burnt wire, either- not only was it offset and the screw not properly clamping it, but might have been insulated from the screw preventing proper contact, too. Poor contact = not enough fault current to trip the breaker + excessive heating = fire.

This isn't an FPE panel, is it?

Top
#176947 - 04/16/08 04:35 PM Re: What caused this situation? [Re: SteveFehr]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Top pic...bad connections, two conductors under 1 screw. Result of low quality workmanship. This design of neutral/ground buss was in GE panels, and the installer had to get the conductor directly under the screw to get a decent termination. Two conductors result in deflection to the sides of the screw, resulting in a poor termination. the poor termination results in a high resistance connection, creating heat on the neutral conductor, and you have a pic of the ultimate end result. This is based on my opinion, and experience.

The second pic, IMHO is an OLD panel that has a corrosion situation. Also, it appears that the two conductors under 1 screw situation is here also.
_________________________
John

Top
#176956 - 04/16/08 08:15 PM Re: What caused this situation? [Re: HotLine1]
WESTUPLACE Offline
Member

Registered: 03/29/04
Posts: 252
Loc: Kingwood, TX USA
Two wires of different gauge in 1 hole. Only one tight.

Top
#176958 - 04/16/08 09:02 PM Re: What caused this situation? [Re: WESTUPLACE]
rhagfo Offline
Member

Registered: 04/16/01
Posts: 44
Loc: Portland, OR. USA
Top Pic Why double lug??? Looks like there a plenty of avaiable unused terminals.

Top
#176963 - 04/17/08 03:11 PM Re: What caused this situation? [Re: rhagfo]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Rhagfo:
Terminating the neutral and ground conductors in one lug, or under 1 screw was a 'trade practice' in some areas. The reasoning was to keep the neutral & grd 'together' for tracing purposes. BTW, not a 'practice' that I have done, nor taught to anyone, but something the 'old-timers' passed on to the 'young guys'.
_________________________
John

Top
#176986 - 04/18/08 03:07 AM Re: What caused this situation? [Re: HotLine1]
Elviscat Offline
Member

Registered: 08/13/05
Posts: 214
Loc: Seattle Washington USA
I'd venture that a loose connection+neutral current on the EGC leads to a burnt/corroded connection. In times gone by it used to be common practice to put 2 neutrals under one screw, this created a definite hazard when one of the circuits is a multiwire, and the other circuit was being removed or serviced.

Top
#176993 - 04/18/08 09:55 AM Re: What caused this situation? [Re: Elviscat]
mikesh Offline
Member

Registered: 06/07/06
Posts: 614
Loc: Victoria, BC, Canada
Current code would of course demand 1 neutral per terminal.
Manufacturers instruction state 1 conductor per terminal for Grounded circuit conductors. The bonding terminal however are allowed 2 #14 or 2 #12 copper or 2#12 or 2#10 aluminum under 1 screw. 1 wire per terminal for larger bonding conductors up to the largest wire permitted for the particular bonding terminal which is often #6. Larger bonding conductors can be accommodated by adding factory approved lugs to the bonding strips or to the enclosure.
I have always followed the 1 neutral 1 screw but until about 10 years ago it was as many bonding wires as would fit as long as we twisted them all together.

Top