What caused this situation? submitted by Joe Tedesco:
|
|
|
|
Joined: Oct 2000
Posts: 2,749
Member
|
Here's another picture of a situation that is constantly questioned by many everywhere! The termination's of the EGC and Grounded (Neutral) conductor.
Joe Tedesco, NEC Consultant
|
|
|
|
Joined: Jul 2004
Posts: 9,931 Likes: 34
Member
|
(ref top pic) A loose connection and an uncleared ground fault? It looks like the bottom conductor wasn't inserted all the way through and missed being clamped by the screw
Greg Fretwell
|
|
|
|
Joined: Mar 2005
Posts: 1,213
Member
|
The panel EGC and neutral look awfully small... And the terminal bus is rusty.
Looks also like the insulation wasn't stripped properly on that burnt wire, either- not only was it offset and the screw not properly clamping it, but might have been insulated from the screw preventing proper contact, too. Poor contact = not enough fault current to trip the breaker + excessive heating = fire.
This isn't an FPE panel, is it?
|
|
|
|
Joined: Apr 2002
Posts: 7,382 Likes: 7
Member
|
Top pic...bad connections, two conductors under 1 screw. Result of low quality workmanship. This design of neutral/ground buss was in GE panels, and the installer had to get the conductor directly under the screw to get a decent termination. Two conductors result in deflection to the sides of the screw, resulting in a poor termination. the poor termination results in a high resistance connection, creating heat on the neutral conductor, and you have a pic of the ultimate end result. This is based on my opinion, and experience.
The second pic, IMHO is an OLD panel that has a corrosion situation. Also, it appears that the two conductors under 1 screw situation is here also.
John
|
|
|
|
Joined: Mar 2004
Posts: 251
Member
|
Two wires of different gauge in 1 hole. Only one tight.
|
|
|
|
Joined: Apr 2001
Posts: 43
Member
|
Top Pic Why double lug??? Looks like there a plenty of avaiable unused terminals.
|
|
|
|
Joined: Apr 2002
Posts: 7,382 Likes: 7
Member
|
Rhagfo: Terminating the neutral and ground conductors in one lug, or under 1 screw was a 'trade practice' in some areas. The reasoning was to keep the neutral & grd 'together' for tracing purposes. BTW, not a 'practice' that I have done, nor taught to anyone, but something the 'old-timers' passed on to the 'young guys'.
John
|
|
|
|
Joined: Aug 2005
Posts: 214
Member
|
I'd venture that a loose connection+neutral current on the EGC leads to a burnt/corroded connection. In times gone by it used to be common practice to put 2 neutrals under one screw, this created a definite hazard when one of the circuits is a multiwire, and the other circuit was being removed or serviced.
|
|
|
|
Joined: Jun 2006
Posts: 613
Member
|
Current code would of course demand 1 neutral per terminal. Manufacturers instruction state 1 conductor per terminal for Grounded circuit conductors. The bonding terminal however are allowed 2 #14 or 2 #12 copper or 2#12 or 2#10 aluminum under 1 screw. 1 wire per terminal for larger bonding conductors up to the largest wire permitted for the particular bonding terminal which is often #6. Larger bonding conductors can be accommodated by adding factory approved lugs to the bonding strips or to the enclosure. I have always followed the 1 neutral 1 screw but until about 10 years ago it was as many bonding wires as would fit as long as we twisted them all together.
|
|
|
Posts: 1,803