#174485 - 02/05/08 06:25 PM Receptacle in drop ceiling?
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
I'm looking for the best method to install receptacles in the middle of a drop ceiling tile.
Caddy & B-Line have brackets to support 4" boxes, but if I install a tile-ring and receptacle, I think the force from inserting the plug will push the whole thing (t-grid and all) upward, resulting in a sloppy installation.

What do you all do?

Thanks
Top
Work Gear for Electricians and the Trades
#174486 - 02/05/08 06:42 PM Re: Receptacle in drop ceiling? [Re: Redsy]
WESTUPLACE Offline
Member
Registered: 03/29/04
Posts: 251
Loc: Kingwood, TX USA
Go to HD or Lowes, get a 24 X 8 Laminated shelf. mount box in shelf, cut 8" off tile, install a cross tee. a few screws thru the frame holds it all in place.
Top
#174489 - 02/05/08 07:58 PM Re: Receptacle in drop ceiling? [Re: Redsy]
Obsaleet Offline
Member
Registered: 04/05/03
Posts: 362
Loc: Pa
Use a self taping screw throught the bracket to the grid. I don't know if it will work with the Caddy 512, as they may be hardened.

Ob
_________________________
Choose your customers, don't let them choose you.
Top
#174495 - 02/06/08 02:49 AM Re: Receptacle in drop ceiling? [Re: Obsaleet]
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
I usually use 7/8" strut to mount the box on and secured the strut to the structure with 1/4" threaded rod.

Roger
Top
#174499 - 02/06/08 05:07 AM Re: Receptacle in drop ceiling? [Re: Roger]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Redsy:
I have used the Caddy with 1/4 rod to prevent upward movement when plugging in.

Ceiling grid is getting flimsier by the week.

_________________________
John
Top
#174508 - 02/06/08 07:47 AM Re: Receptacle in drop ceiling? [Re: HotLine1]
Gregtaylor Offline
Member
Registered: 03/02/05
Posts: 212
Loc: Boise, Idaho, USA
I cut a piece of 3/8 plywood to the size of the ceiling tile. I put it right on top of the ceiling tile and use a 1" plaster ring on a 4" box supported by a Caddy 512. The plywood lends weight and stiffness to the whole thing. Keep in mind that ceiling plugs usually get 1 item plugged in and it stays there. They are rarely used as true convenience receps.
Top
#174549 - 02/07/08 07:14 PM Re: Receptacle in drop ceiling? [Re: Redsy]
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Thanks for all your ideas guys!
I wondered if the grid was heavy enough to prevent upward movement.
I appreciate your input.
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 93 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals