The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Today at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 8
Trumpy 6
Who's Online
0 registered (), 139 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#17218 - 11/21/02 07:22 PM adding circuits to a panel that is not accessible
mj Offline
Member

Registered: 06/10/02
Posts: 188
Loc: meriidian, ms
guys, any tricks to adding circuits to a panel that is not accessible? besides cutting holes in the sheet rock or fishing, in other way of getting into the panel to add more circuits ?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#17219 - 11/21/02 07:32 PM Re: adding circuits to a panel that is not accessible
CTwireman Offline
Member

Registered: 02/07/02
Posts: 839
Loc: Connecticut, USA
Wiremold?

I use a "snaking trick" that is pretty effective in these situations. I know you said "besides snaking" but I dont know how you could avoid it (besides surface wiring).

I take a roll of mason's string and tie a heavy nut or screw on the end. I then dump a pile of string into the wall cavity (the string just falls into the wall space by gravity). I then take my metal fish tape and grab the string from the other end.

I'm sure you have all heard of this trick but for anyone that hasn't, it can be a real lifesaver. It's really great when working alone.
_________________________
Peter

Top
#17220 - 11/21/02 07:44 PM Re: adding circuits to a panel that is not accessible
mj Offline
Member

Registered: 06/10/02
Posts: 188
Loc: meriidian, ms
ctwireman, thanks for the wiremold idea, i did not think of wiremold as a raceway from a panel .

Top
#17221 - 11/21/02 07:49 PM Re: adding circuits to a panel that is not accessible
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Caution:

Using anything metal for snaking into a panel can prove to be very hazardous.

Bill

Top
#17222 - 11/21/02 08:02 PM Re: adding circuits to a panel that is not accessible
mj Offline
Member

Registered: 06/10/02
Posts: 188
Loc: meriidian, ms
roger that, bill, i dont like fishing into live panels,

Top
#17223 - 11/21/02 08:03 PM Re: adding circuits to a panel that is not accessible
CTwireman Offline
Member

Registered: 02/07/02
Posts: 839
Loc: Connecticut, USA
Yes, of course, ALWAYS de-energize before using this method, even if you have to pull the meter.

I don't like to snake into live enclosures but have had to do it on occasion (with someone on the other end of course!)

[This message has been edited by CTwireman (edited 11-21-2002).]
_________________________
Peter

Top
#17224 - 11/22/02 01:28 PM Re: adding circuits to a panel that is not accessible
RandyO Offline
Member

Registered: 09/26/02
Posts: 28
As an old cable puller from way back, my boss used to always say, why thread that needle twice.

unless you are the VERY FIRST one to pull an add on, ddisconnect someone elses and use it as a pull cord for yours.

But that brings a new question to mind.
lets say I fish a new 12/2 romex wire through the wall from the attic. and connect it into the pannel board.

did I just violate the wire securing rule of 12" from the pannel board.??? posibliy the 4.5 ft rule????

good questions, any inspectors out there???

Top
#17225 - 11/22/02 01:48 PM Re: adding circuits to a panel that is not accessible
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
The panel covers 1/2" overlap has been an asset to me here....


RandyO, check 334.30(B)(1)

Top
#17226 - 11/22/02 07:49 PM Re: adding circuits to a panel that is not accessible
sparky66wv Offline
Member

Registered: 11/17/00
Posts: 2339
Loc: West Virginia
Steve, Yup, that's how I do it... Cut as close to the edge of the cover as you can...

How else to tighten the NMC Connector screws?
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

Top
#17227 - 11/23/02 07:18 AM Re: adding circuits to a panel that is not accessible
gto6t7 Offline
Member

Registered: 12/16/00
Posts: 30
Loc: Machias, ME
What I do after running romex into the panel is use a plastic romex connector, the type that has a small wedge to secure the wire, and put it on the wire backwards, then I snap it into the knockout from inside the panel. Now the wire has a secure safe connection. No one ever said these connectors had to be on the outside and it eliminates the problem trying to get a locknut on a metal connector. BTW my fiberglass fish-sticks are a lifesaver doing this type of work!

[This message has been edited by gto6t7 (edited 11-23-2002).]