#170844 - 11/13/07 02:02 PM #12 THHN in 3/4" conduit.
Trick440 Offline
Member
Registered: 08/15/05
Posts: 247
Loc: Waterford, MI, USA
How are most guys doing this? What I'm hearing is only pull 3 #12 curcuits in 3/4" conduit. Is this what most guys are doing?

Please correct my math. If I pulled more, say 9 current carrying #12 conductors. Than it would be 2400w, derated to 1680w. So I could load the circuit up to 1680w.. (taking into consideration continuous loads)

I would like to know what most guys are doing. My background is residential, commercial is a different animal I'm still trying to grasp.

Thanks.
_________________________
Shake n Bake
Top
Work Gear for Electricians and the Trades
#170846 - 11/13/07 03:05 PM Re: #12 THHN in 3/4" conduit. [Re: Trick440]
Trick440 Offline
Member
Registered: 08/15/05
Posts: 247
Loc: Waterford, MI, USA
I did a search and figured it out.

9 current carrying conductors, neutrals count as current carrying.. Would keep #12 rated for 20amps. So 4 circuits in a 3/4"
_________________________
Shake n Bake
Top
#170850 - 11/13/07 05:02 PM Re: #12 THHN in 3/4" conduit. [Re: Trick440]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
You could put 4 multiwire single phase circuits in a conduit. That looks like 8 circuits at 120v.
310.15(B)(4)(a)
If you didn't have any harmonic loads it could be 3 3p wye multiwires for 9 120v circuits.
_________________________
Greg Fretwell
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 87 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals