How are most guys doing this? What I'm hearing is only pull 3 #12 curcuits in 3/4" conduit. Is this what most guys are doing?

Please correct my math. If I pulled more, say 9 current carrying #12 conductors. Than it would be 2400w, derated to 1680w. So I could load the circuit up to 1680w.. (taking into consideration continuous loads)

I would like to know what most guys are doing. My background is residential, commercial is a different animal I'm still trying to grasp.

Thanks.


Shake n Bake