#143132 - 05/12/05 04:13 PM AC insulation resistance tester
lyledunn Offline
Member
Registered: 06/30/02
Posts: 159
Loc: N.Ireland
Have any of you guys used an ac insulation resistance tester?
_________________________
regards

lyle dunn
Top
Test Equipment:
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
#143133 - 05/12/05 06:22 PM Re: AC insulation resistance tester
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
Yes lyle,
I use one every once in a while here.
I take it that you are talking about a Hi-Pot test (or Dielectric Withstand Test), as opposed to the plain-vanilla DC Insulation Resistance test?.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
#143134 - 05/14/05 05:26 AM Re: AC insulation resistance tester
lyledunn Offline
Member
Registered: 06/30/02
Posts: 159
Loc: N.Ireland
Yes Trumpy, thanks for the reply.
I know that they are required for dielectric testing of certain products and electrical systems. An output of 3750vac even though current limited is not appropriate in the wrong hands.
What I wanted to know was if these instruments had a place in the field rather than in the production line lab.
_________________________
regards

lyle dunn
Top
#143135 - 05/14/05 06:16 AM Re: AC insulation resistance tester
chipmunk Offline
Member
Registered: 07/20/04
Posts: 144
Loc: Southampton, UK
Way back in the last century, (ok 12 years ago) I had to use such a beast as part of the portable appliance testing regime where I worked. Output as you say, up to 3750 volts AC, current limited to 5/10/15 mA, selected by a switch, with a deeply recessed "operate" button so it couldn't be energized accidentally. I agree they should only be used by competent persons trained in the dangers of high voltage.
With a probe carrying that kind of voltage, you could do a lot of damage to some kinds of electronic devices. But it helped pick up deteriorating insulation on double insulated tools and appliances, so yes, I believe they do have a place in the field, just a very narrowly defined one.
Top
#143136 - 05/18/05 06:05 AM Re: AC insulation resistance tester
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
Lyle,
We have a 20kV model here at the PoCo, it's used for flash testing HV cables, transformers and switch-gear, as well as the odd suspect bushing insulator.
I agree fully with yourself and Chipmunk, 3.75kV is not the sort of cat you want to let out of the bag, these voltages are lethal with the most minute of current levels.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 84 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals