The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 252 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#12926 - 08/21/02 04:11 PM Opinion needed
Jim M Offline

Registered: 08/10/01
Posts: 453
Loc: Chestertown, MD, USA
This was posted on a DIY site. I don't see how Article 312 would apply to a sleeve for NM-B running to a surface mounted device ie switch or receptacle. Your thoughts?

We commonly 'sleeve' romex NM-B cable from a suface mounted wall box ...and it extends up into a joist space...and does not penetrate any of the structure.This saves us from installing a splice box up there!

The conduit is generally a straight piece and extends up into the joist space,and MUST have a protective bushing on that far end.

A complete conduit system is defined as one with enclosures etc at each end.

A 24" short nipple between two enclosures ,and no longer than 24" is permotted to be filled at 60% of its it is apart of a complete system.
This would require a trade size conduit of no less than 3/4" for a 12-2G NM-B cable.

Your installation is not a complete system...and the 1/2" conduit is fine,[I prefer 3/4" for this ] if between 18" and not longer than 10ft..and if it is also secured at the far end...if the NM-B was installed without trauma...a bushing is installed and the opening sealed as per 312-5.c.d...and the cable is stapled within 12" of the exit point in that joist space...

I have always used a bushing and properly secured the cable, but don't see the purpose of the raceway seal. I don't know how the moderator thinks that this Article would apply as this is not entering a cabinet, cutout or meter socket.

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#12927 - 08/21/02 05:35 PM Re: Opinion needed
ElectricAL Offline

Registered: 10/10/01
Posts: 615
Loc: Minneapolis, MN USA
I agree with you, Jim. Seems to me that 300.4 is the appropriate reference.