#103046 - 03/10/02 06:07 AM What's Wrong Here?
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA


This picture shows violations of a rule in the 2002 NEC in Article 312, can you describe what they are?
_________________________
Joe Tedesco, NEC Consultant
Top
2017 / 2014 NEC & Related Books and Study Guides
#103047 - 03/10/02 04:49 PM Re: What's Wrong Here?
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
{From 312.5(C) EX..}
(d) The raceway is sealed or plugged at the outer end using approved means so as to prevent access to the enclosure through the raceway.
(e) The cable sheath is continuous through the raceway and extends into the enclosure beyond the fitting not less than 6 mm (1/4 in.).
(f) The raceway is fastened at its outer end and at other points in accordance with the applicable article.
(g) Where installed as conduit or tubing, the allowable cable fill does not exceed that permitted for complete conduit or tubing systems by Table 1 of Chapter 9 of this Code and all applicable notes thereto.
FPN:See Table 1 in Chapter 9, including Note 9, for allowable cable fill in circular raceways. See 310.15(B)(2)(a) for required ampacity reductions for multiple cables installed in a common raceway.

I've better luck in a 'captive' panel with these..
Top
#103048 - 03/10/02 05:02 PM Re: What's Wrong Here?
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1457
Loc: Holden, MA USA
Besides all that mess I would bet the connector on the ser is not correct. Looks like an seu connector.
Top
#103049 - 03/12/02 02:15 PM Re: What's Wrong Here?
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
Sure is a long list of what to do to comply and the connector looks like the wrong one as you mentioned.


[This message has been edited by Joe Tedesco (edited 08-10-2002).]
_________________________
Joe Tedesco, NEC Consultant
Top
#103050 - 03/15/02 03:55 AM Re: What's Wrong Here?
Trainwire Offline
Member
Registered: 03/15/02
Posts: 360
Loc: Strasburg,PA,USA
Um, I have seen this before (my mother in laws place actually,) but it looks like there are more than one wire per screw in the neutral bar, refer to the previous thread.

Thanks for letting me join.

trainwire
Top
#103051 - 03/15/02 08:39 AM Re: What's Wrong Here?
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
I know that it is a violation to bring all of the cables into the 2" PVC male adapter, but where is the hazard in the installation?
Don(resqcapt19)
_________________________
Don(resqcapt19)
Top
#103052 - 03/15/02 03:24 PM Re: What's Wrong Here?
nesparky Offline
Member
Registered: 06/21/01
Posts: 642
Loc: omaha,ne
I do not see a hazard. This was done in many houses and apartments for years. Then the code changed in 1999. Never did see or hear of a actual real world reason for the change.
oh well life goes on
_________________________
ed
Top
#103053 - 03/15/02 04:34 PM Re: What's Wrong Here?
Fred Offline
Member
Registered: 04/30/01
Posts: 449
Loc: Straughn, IN 47387
Manufactured houses are still coming from the factory like this. And they carry the HUD label. 2 story homes come with a 2" PVC from the panel to the attic with the 2nd story home runs rolled up in the attic section ready to be stuffed down the pipe as per the wiring instructions that come with the home.
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6775
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 55 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals