#102467 - 03/18/06 10:11 PM Useage of lag type emily knobs
bigpapa Offline
Member
Registered: 03/18/06
Posts: 77
Loc: canada
Seems that 6-112 (6) calls for a bolted service wire support. Is this enforced in your city? I have an old house to change the service and an Emily know would work fine. Why do I have to rip open the walls just to put in a bolt?
Top
Tools for Electricians:
#102468 - 03/19/06 09:00 AM Re: Useage of lag type emily knobs
jay8 Offline
Member
Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
I have done services in Vancouver using the lag bolt type emily knob, even called up the inspection department before I installed. They told me the lag bolt type was acceptable, everything passed.
Top
#102469 - 03/19/06 10:56 AM Re: Useage of lag type emily knobs
dougwells Offline


Member
Registered: 05/03/03
Posts: 1137
Loc: kamloops BC Canada
In British Columbia we must use the bolt with washer and Nut. we cannot use the screw in type insulator. This is also a BC Hydro requirement.
Top
#102470 - 04/05/06 08:57 PM Re: Useage of lag type emily knobs
bigpapa Offline
Member
Registered: 03/18/06
Posts: 77
Loc: canada
I phoned the provincial inspector here in B.C. and he said they accept them but only if screwed into solid wood all the way.
Top
#102471 - 04/06/06 04:51 AM Re: Useage of lag type emily knobs
jay8 Offline
Member
Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
funny this came up, recently I did a renovation on an older home, but fairly recent service upgrade. The emily knob had been pulled right out of the exterior wall, conductors were suspended by the crimp connections. This was the lag type, no doubt just screwed into the siding and sheathing. 6-112(6) does specify bolts, I guess the interpretation by some jurisdictions is 'lag bolt', not lag screw.
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (annemarie1), 67 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals