#102322 - 01/18/06 09:46 AM mineral insulated cable
student Offline
Junior Member
Registered: 01/08/06
Posts: 6
Hi

Does anyone know what is max support of the above cable in hazardous location.It is not 2m for sure.Thanks
Top
Tools for Electricians:
#102323 - 01/18/06 05:17 PM Re: mineral insulated cable
RobbieD Offline
Member
Registered: 02/23/03
Posts: 231
Loc: Canada
As far as I can see in the CEC it only says

12-706(2) secured at intervals not exceeding 2m

I can't find anything in the code talking about different supporting intervals in hazardous locations for MI cable.

Anyone else out there know if there are any other rules on this matter?
Top
#102324 - 01/19/06 06:47 PM Re: mineral insulated cable
RobbieD Offline
Member
Registered: 02/23/03
Posts: 231
Loc: Canada
I think that I found what you are looking for. Look in Appendix J.
J18-062(2)(a) on pg 487.
It says not more than 1.8m
Top
#102325 - 01/19/06 06:57 PM Re: mineral insulated cable
Sandro Offline
Member
Registered: 12/30/01
Posts: 444
Loc: Stoney Creek, ON, Canada
hehehe.....that's one of those trick questions the code teacher threw at us in class. Answer is located in one of the obscure tables.
Top
#102326 - 01/19/06 11:55 PM Re: mineral insulated cable
student Offline
Junior Member
Registered: 01/08/06
Posts: 6
Answer is located in one of the obscure tables.
Way do not you say if you know.This is trade for good for all of us.It looks to me we are playing hide and seek.Rgards
Top
#102327 - 01/20/06 09:09 AM Re: mineral insulated cable
Rick Kelly Offline
Member
Registered: 01/11/06
Posts: 60
Loc: Iqaluit, NU, Canada
This is a good one. If the MI cable is single conductor in a harzardous location then 18-062(2)(a) applies. If it is multi-conductor MI cable, in a hazardous location, then 18-062(2)(a) does not apply and 12-706(2) does. This is to prevent sheath currents from being a problem in a hazardous area. If it is a non-hazardous area then 12-706(2) applies wether the cable is a single or multi conductor.
Top
#102328 - 01/20/06 07:47 PM Re: mineral insulated cable
Sandro Offline
Member
Registered: 12/30/01
Posts: 444
Loc: Stoney Creek, ON, Canada
Welcome aboard Rick! Sure is nice to see the canuck board growing.
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 49 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals