1 members (Scott35), 468 guests, and 12 robots.
#102322 01/18/06 01:46 PM
student Offline OP
Hi
Does anyone know what is max support of the above cable in hazardous location.It is not 2m for sure.Thanks
#102323 01/18/06 09:17 PM
As far as I can see in the CEC it only says
12-706(2) secured at intervals not exceeding 2m
I can't find anything in the code talking about different supporting intervals in hazardous locations for MI cable.
Anyone else out there know if there are any other rules on this matter?
#102324 01/19/06 10:47 PM
I think that I found what you are looking for. Look in Appendix J.
J18-062(2)(a) on pg 487.
It says not more than 1.8m
#102325 01/19/06 10:57 PM
hehehe.....that's one of those trick questions the code teacher threw at us in class. Answer is located in one of the obscure tables.
#102326 01/20/06 03:55 AM
student Offline OP
Way do not you say if you know.This is trade for good for all of us.It looks to me we are playing hide and seek.Rgards
#102327 01/20/06 01:09 PM
This is a good one. If the MI cable is single conductor in a harzardous location then 18-062(2)(a) applies. If it is multi-conductor MI cable, in a hazardous location, then 18-062(2)(a) does not apply and 12-706(2) does. This is to prevent sheath currents from being a problem in a hazardous area. If it is a non-hazardous area then 12-706(2) applies wether the cable is a single or multi conductor.
#102328 01/20/06 11:47 PM
Welcome aboard Rick! Sure is nice to see the canuck board growing.