The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 186 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#102259 - 12/13/05 07:48 PM Cable under a roadway
Cinner Offline
Member

Registered: 12/01/04
Posts: 77
Loc: Kelowna, B.C., Canada
How deep would you have to bury a 5000 volt acwu cable under a roadway. Does anyone know what section or rule pertains to this in the cec?

Top
2014 / 2011 NEC & Related Books and Study Guides
#102260 - 12/14/05 11:18 AM Re: Cable under a roadway
dougwells Offline

Member

Registered: 05/03/03
Posts: 1228
Loc: kamloops BC Canada
Section 36 deals with HV installations but I can only see where it mentions in a building , not underground distribution at all. But it says it has to be marked every 3 meters

Top
#102261 - 12/14/05 04:50 PM Re: Cable under a roadway
YORKIE Offline
Member

Registered: 11/24/05
Posts: 20
Loc: abbotsford.bc
Section 12
Rule 12-012 Appendix B and table 53.This says 1000mm. If you have any doubts check with your local inspector

Top
#102262 - 12/14/05 05:05 PM Re: Cable under a roadway
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
I don't know beans about the Canadian code... and I consider 480v to be "high voltage."

However, I suspect my local utility would require such a line to be buried at least 5 ft. deep, especially if there was no other protection (such as pipe).

Top
#102263 - 06/20/06 09:45 AM Re: Cable under a roadway
mikesh Offline
Member

Registered: 06/07/06
Posts: 614
Loc: Victoria, BC, Canada
From Table 53 conductors over 750 volts must be buried a minimum of 1 meter or 39 1/2 inches for the metrically challenged.
High voltage is over 750 volts so the 480 volts is "low" voltage.