ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/22/24 10:36 AM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 220 guests, and 11 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#102259 12/13/05 11:48 PM
Joined: Dec 2004
Posts: 78
C
Cinner Offline OP
Member
How deep would you have to bury a 5000 volt acwu cable under a roadway. Does anyone know what section or rule pertains to this in the cec?

#102260 12/14/05 03:18 PM
Joined: May 2003
Posts: 1,158
Member
Section 36 deals with HV installations but I can only see where it mentions in a building , not underground distribution at all. But it says it has to be marked every 3 meters

#102261 12/14/05 08:50 PM
Joined: Nov 2005
Posts: 20
Y
Member
Section 12
Rule 12-012 Appendix B and table 53.This says 1000mm. If you have any doubts check with your local inspector

#102262 12/14/05 09:05 PM
Joined: Jan 2005
Posts: 5,445
Likes: 3
Cat Servant
Member
I don't know beans about the Canadian code... and I consider 480v to be "high voltage."

However, I suspect my local utility would require such a line to be buried at least 5 ft. deep, especially if there was no other protection (such as pipe).

#102263 06/20/06 12:45 PM
Joined: Jun 2006
Posts: 613
M
Member
From Table 53 conductors over 750 volts must be buried a minimum of 1 meter or 39 1/2 inches for the metrically challenged.
High voltage is over 750 volts so the 480 volts is "low" voltage.


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5