#101834 - 09/27/03 12:33 PM Elevator disconnect
kitha Offline
Member
Registered: 11/12/02
Posts: 12
Loc: Hamilton, ON, Canada
I understand that that as per Canadian electrical code section 38, elevator needs a fused(ttype D) disconnect switch inside the machine room. I have an application where the elevator is fed from a remote breaker panel via the disconnect inside the room. What are the requirements/considerations to select the remote breaker. I guess it needs to be selectively coordinated with the fused disconnect switch in case of a fault.
Top
Tools for Electricians:
#101835 - 09/28/03 03:02 PM Re: Elevator disconnect
Tony Moscioni Offline
Moderator
Registered: 05/15/01
Posts: 144
Loc: CANADA
Rationale for Rule 38-034.

Where there are other disconnects upstream controlling power to the elevator machine room, these shall be coordinated to ensure that any fault in the elevator system will trip the disconnect in the elevator room. Under some circumstances, in large machine rooms with multiple machines and controllers, additional switches are required for the protection of elevator service personnel.

Intent for Rule 38-034

We intend that the disconnecting means for all elevator circuits be in the machine room readily accessible to elevator service personnel—for whose protection each disconnecting means shall be plainly marked and lockable in the open position. Escalator disconnect switches shall be located in the same location as the controller.

Tony Moscioni
Electrical Inspector
Electrical SDafety Authority
Top
#101836 - 09/28/03 03:26 PM Re: Elevator disconnect
Bjarney Offline
Moderator
Registered: 04/10/02
Posts: 2527
Loc: West-Southern Inner-Northeast ...
Hasn't the been adequately covered yesterday and today at http://www.eng-tips.com/viewthread.cfm?SQID=72839&SPID=238&page=1 ?
Top
#101837 - 09/28/03 09:28 PM Re: Elevator disconnect
kitha Offline
Member
Registered: 11/12/02
Posts: 12
Loc: Hamilton, ON, Canada
Hi Tony! Thanks for the rationale. In CEC or any commonly applied by-laws, are there any other situations that fused disconnects are mandatory? Why can't we use non fused disconnects?
Top
#101838 - 10/07/03 07:30 PM Re: Elevator disconnect
kitha Offline
Member
Registered: 11/12/02
Posts: 12
Loc: Hamilton, ON, Canada
Upon nobody's reply to my question and with my later findings/hearings from close friends I would like to know if there's any UL requirement that fused disconnect switches are mandatory for air conditioning machines and whatever that do not have built in overload protecion.
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 48 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals