The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm² flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 186 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#101834 - 09/27/03 12:33 PM Elevator disconnect
kitha Offline
Member

Registered: 11/12/02
Posts: 10
Loc: Hamilton, ON, Canada
I understand that that as per Canadian electrical code section 38, elevator needs a fused(ttype D) disconnect switch inside the machine room. I have an application where the elevator is fed from a remote breaker panel via the disconnect inside the room. What are the requirements/considerations to select the remote breaker. I guess it needs to be selectively coordinated with the fused disconnect switch in case of a fault.

Top
2014 / 2011 NEC & Related Books and Study Guides
#101835 - 09/28/03 03:02 PM Re: Elevator disconnect
Tony Moscioni Offline
Moderator

Registered: 05/15/01
Posts: 144
Loc: CANADA
Rationale for Rule 38-034.

Where there are other disconnects upstream controlling power to the elevator machine room, these shall be coordinated to ensure that any fault in the elevator system will trip the disconnect in the elevator room. Under some circumstances, in large machine rooms with multiple machines and controllers, additional switches are required for the protection of elevator service personnel.

Intent for Rule 38-034

We intend that the disconnecting means for all elevator circuits be in the machine room readily accessible to elevator service personnel—for whose protection each disconnecting means shall be plainly marked and lockable in the open position. Escalator disconnect switches shall be located in the same location as the controller.

Tony Moscioni
Electrical Inspector
Electrical SDafety Authority

Top
#101836 - 09/28/03 03:26 PM Re: Elevator disconnect
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
Hasn't the been adequately covered yesterday and today at http://www.eng-tips.com/viewthread.cfm?SQID=72839&SPID=238&page=1 ?

Top
#101837 - 09/28/03 09:28 PM Re: Elevator disconnect
kitha Offline
Member

Registered: 11/12/02
Posts: 10
Loc: Hamilton, ON, Canada
Hi Tony! Thanks for the rationale. In CEC or any commonly applied by-laws, are there any other situations that fused disconnects are mandatory? Why can't we use non fused disconnects?

Top
#101838 - 10/07/03 07:30 PM Re: Elevator disconnect
kitha Offline
Member

Registered: 11/12/02
Posts: 10
Loc: Hamilton, ON, Canada
Upon nobody's reply to my question and with my later findings/hearings from close friends I would like to know if there's any UL requirement that fused disconnect switches are mandatory for air conditioning machines and whatever that do not have built in overload protecion.