Rationale for Rule 38-034.
Where there are other disconnects upstream controlling power to the elevator machine room, these shall be coordinated to ensure that any fault in the elevator system will trip the disconnect in the elevator room. Under some circumstances, in large machine rooms with multiple machines and controllers, additional switches are required for the protection of elevator service personnel.
Intent for Rule 38-034
We intend that the disconnecting means for all elevator circuits be in the machine room readily accessible to elevator service personnel—for whose protection each disconnecting means shall be plainly marked and lockable in the open position. Escalator disconnect switches shall be located in the same location as the controller.
Tony Moscioni
Electrical Inspector
Electrical SDafety Authority