ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#100808 - 01/08/07 04:13 PM 220-volt counter top appliance... GFI?
Jps1006 Offline
Member
Registered: 01/22/04
Posts: 615
Loc: Northern IL
In addition to my required kitchen countertop circuit, the customer wants a 220-volt receptacle for an Italian appliance. This is similar to a toaster or something, but 220-volt. Am I not required by NEC to GFI protect?

What do they do in Europe? are they required to protect kitchen counter top receptacles with GFI's?
Top
2017 / 2014 NEC & Related Books and Study Guides
#100809 - 01/08/07 04:40 PM Re: 220-volt counter top appliance... GFI?
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
210.8(A) All 125 volt.......
No GFI required.

But look out.

210.6(A)(2)Limits the voltage in dwellings to nominal 120 volts for cord-and-plug-connected loads of 1,440VA or less, or less than 1/4 hp.
Top
#100810 - 01/08/07 06:14 PM Re: 220-volt counter top appliance... GFI?
EV607797 Offline
Member
Registered: 10/25/06
Posts: 744
Loc: Fredericksburg, VA, USA
That is an excellent question. I have never encountered such a situation. I guess you learn something new every day.
_________________________
---Ed---

"But the guy at Home Depot said it would work."
Top
#100811 - 01/08/07 07:02 PM Re: 220-volt counter top appliance... GFI?
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Excellent answer also. I've run into this a coupla time when people want to use "portable" kitchen appliances like toaster and coffee brewers that they bring her from out of the US.
_________________________
George Little
Top
#100812 - 01/08/07 08:03 PM Re: 220-volt counter top appliance... GFI?
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I don't see a huge hazard. Canada has mandated multiwire, split receptacles in the kitchen for years and they don't have a huge body count. That is still 240v on a single yoke. If the customes says he thinks the "kettle" is about 1500w the code problem goes away. I seem to recall the Brits use some pretty hefty kettles.
Nobody wants to wait too long for their tea.

Being Italian it may be an expresso machine.

[This message has been edited by gfretwell (edited 01-08-2007).]
_________________________
Greg Fretwell
Top
#100813 - 01/09/07 06:44 AM Re: 220-volt counter top appliance... GFI?
Mike Wescoatt Offline
Member
Registered: 06/17/01
Posts: 161
Loc: Cedar City, Utah
OK, why not do it? It isn't likely to do much false tripping, and might save someone's life. $60 breaker vs. electrocution. Code is a minimum, not recommended design practice. What is the intent behind this part of the code?

How many homes have you done lately with the code minimum lighting?

Thanks... I'm done now. :-)
_________________________
Mike Wescoatt
Top
#100814 - 01/09/07 08:59 AM Re: 220-volt counter top appliance... GFI?
mikesh Offline
Member
Registered: 06/07/06
Posts: 613
Loc: Victoria, BC, Canada
I find it interesting that it has taken the CEC until the 2006 edition to mandate GFCI protection around kitchen sinks and frankly don't really think that is necessary. I guess somewhere someone has been electrocuted in the kitchen by touching a faulty appliance and the sink. or washed a plugged in toaster. The CEC only requires GFCI protection for 15 and 20 amp receptacles. In Canada at least the Italian 230 volt, Pannini maker could have a receptacle installed without gfci protection. Now whether or not the appliance needs a special approval will depend on the lable on the appliance. Perhaps there is a standard that would not approve a counter top toaster operating at 230 volts for home use.
Incidently if for example a coffe maker was installed on the counter and was connected in such a way where it could not be easily moved on the counter, then if the receptacle was located behind the coffee maker it would not require GFCI protection.
Top
#100815 - 01/09/07 02:25 PM Re: 220-volt counter top appliance... GFI?
RobbieD Offline
Member
Registered: 02/23/03
Posts: 231
Loc: Canada
In Ontario,Canada it is required to have all receptacles, that are located in kitchens and installed within 1m of a kitchen sink, protected by a GFCI. So if this appliance was within this distance it would need to be protected.

The CEC which, covers different provinces in Canada states that only 120V, 15 and 20 amp receptacles require this.

When I was overseas almost every panel that I worked in had those residual current devices. The buildings that I worked in were small. Sorta sucked troubleshooting because if a neutral in any circuit would touch ground the main would trip.

The appliance will most likely require approval for use in the US by the AHJ.

Myself I would GFCI it if it was close to the sink, if its located somewhere else then I wouldn't.

Wish I knew more about the US codes to help you out.



[This message has been edited by RobbieD (edited 01-09-2007).]
Top
#100816 - 01/09/07 03:52 PM Re: 220-volt counter top appliance... GFI?
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Where do AHJ's approve appliances? If it is not fixed in place when the AHJ issues the CO they couldn't care less what a homeowner brings in later.
_________________________
Greg Fretwell
Top
#100817 - 01/09/07 04:59 PM Re: 220-volt counter top appliance... GFI?
RobbieD Offline
Member
Registered: 02/23/03
Posts: 231
Loc: Canada
I'm not sure about the approval marking thing. All I know is that it is illegal here in Canada to sell an electrical appliance that is not listed by one of the approved agencies.
I just always assumed that the insurance company would give you a hard time if your house burnt down and they concluded that the cause was an appliance fire from an unlisted appliance that you knew wasn't listed by an approved agency.

But I guess they give you a hard time about all claims anyway.
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals