#100073 - 10/10/06 05:12 AM Dual Rated Direct Burial Service Entrance Cable
Happi_Man Offline
Member
Registered: 06/12/02
Posts: 206
Loc: Columbus, Ohio - USA
Under what "name" do I find this cable. Basically a fire rated URD. This is for onstallation of a residential service from a disconnect/meter at a pole to go directly into the house and to the main panel.

Is the cable I should be looking for RHH and/or RHW or is there something different???

Thanks.
Mike
Top
2017 / 2014 NEC & Related Books and Study Guides
#100074 - 10/10/06 06:15 AM Re: Dual Rated Direct Burial Service Entrance Cable
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
URD is Underground Residential Distribution.
A medium voltage (15KV- 35KV) cable used for underground residential transformer feeders.

Do you mean to say USE?
_________________________
Earl
Top
#100075 - 10/10/06 07:33 AM Re: Dual Rated Direct Burial Service Entrance Cable
Happi_Man Offline
Member
Registered: 06/12/02
Posts: 206
Loc: Columbus, Ohio - USA
What I am looking for is a URD type cable that I can take directly into the house to the panel. But yes I guess I mean USE as the URD terminology is not really used anymore.

Inspector is telling me that I cannot use USE to go from to pole where the meter/disconnect is mounted directly into the house to the panel (in conduit). That I have to use a fire rated type USE.

I guess my question is whether or not that is RHH and/or RHW and where in the code can I find more info on this situation?

Thanks
Top
#100076 - 10/10/06 11:10 AM Re: Dual Rated Direct Burial Service Entrance Cable
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
The UL listing for SERVICE CABLE (TXKT) is the place to determine the acceptability of your cable. USE cables cannot enter inside, as they have no fire/smoke rating.

UL lists Types USE and USE-2 cables for underground installation including direct burial. But, they are not suitable for use in premises or aboveground except to terminate at the service equipment or metering equipment.

The UL listing includes the following: "Type USE cable contains conductors with insulation equivalent to RHW or THHW."

Sounds like you need to either change wiring just outside the house, or terminate at the meter enclosure, then change to SE cable prior to entering the house.
_________________________
Earl
Top

Member Spotlight
Member Since: 10/07/00
Posts: 3417
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals