Posted By: ccdave conduit between buildings - 03/01/06 11:34 PM
Can any of you help me with locating a code(I thought I saw it and can't remember where) that prohibits ridged conduit from eva to eve between to detached buildings
thanks--dave
Posted By: tdhorne Re: conduit between buildings - 03/01/06 11:58 PM
If the length of the rigid between the supports is less than ten feet it is legal.
Posted By: ccdave Re: conduit between buildings - 03/02/06 12:44 AM
Let me correct my self--Its sch.40 pvc
Posted By: ccdave Re: conduit between buildings - 03/02/06 12:46 AM
let me correct myself--it's sch 40pvc
Posted By: gfretwell Re: conduit between buildings - 03/02/06 02:45 AM
This is the max span between supports
1/2–1" 3ft
11/4–2" 5ft
21/2–3" 6ft
31/2–5" 7ft
6" 8ft
Posted By: Alan Nadon Re: conduit between buildings - 03/02/06 04:46 PM
The span table is from NEC 352.30 (B) the next section list expansion fittings 352.44 NEC which may be required for this installation.
Being in California it might be recommended to use a flexible raceway between buildings.
Alan--
Posted By: Celtic Re: conduit between buildings - 03/02/06 09:12 PM
opps

[This message has been edited by Celtic (edited 03-02-2006).]