Posted By: aldav53 outdoor spa recepticle - 03/01/02 03:34 AM
Is it legal to have a 20a 120v single recepticle outdoors "not GFI protected", for a spa if the spa has its own GFI built into the plug? Does the recept have to be 5 feet away from the spa?
Posted By: Redsy Re: outdoor spa recepticle - 03/01/02 02:19 PM
I believe the only exception to GFCI protection for 120 volt receptacles in dwellings is for de-icing equipment. No one knows if someone will unplug the spa and plug in a hedge clipper at some point.

[This message has been edited by Redsy (edited 03-01-2002).]
Posted By: HIGHVOLTAGE Re: outdoor spa recepticle - 03/02/02 06:19 AM
aldav53
680 !
part VI 680.40 ,,,680.42 then in partII read 680.22(a)(4) that should be enough for ya!