#7943 02/28/02 11:34 PM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
Is it legal to have a 20a 120v single recepticle outdoors "not GFI protected", for a spa if the spa has its own GFI built into the plug? Does the recept have to be 5 feet away from the spa?


The Golden Rule - "The man with the gold makes the rule"
#7944 03/01/02 10:19 AM
Joined: Mar 2001
Posts: 2,056
R
Member
I believe the only exception to GFCI protection for 120 volt receptacles in dwellings is for de-icing equipment. No one knows if someone will unplug the spa and plug in a hedge clipper at some point.

[This message has been edited by Redsy (edited 03-01-2002).]

#7945 03/02/02 02:19 AM
Joined: Feb 2002
Posts: 38
H
Member
aldav53
680 !
part VI 680.40 ,,,680.42 then in partII read 680.22(a)(4) that should be enough for ya!